    Guys this is a particular assembly out of my estimating program. When using insulated connectors I wouldn't need the plastic bushing, correct? Don't know why they included it.


    1 1/4" CONDUIT - EMT 40.00
    1 1/4" COUPLING SS STL - EMT 4.00
    1 1/4" CONN SS STL INSUL - EMT 8.00
    1 1/4" BUSHING - PLASTIC 8.00
    1 1/4" 1-H STRAP - EMT - STEEL 4.00
    1/4-20x 1 3/4 WEDGE ANCHOR - 1 1/8" MIN DEPTH 4.00
    # 2 THHN BLACK 216.00
    # 8 THHN BLACK 54.00
    # 2 WIRE POWER TERM 32.00
    # 8 WIRE POWER TERM 8.00

  2. #2
    Join Date
    Jan 2009
    Location
    Maryland
    Posts
    12,404
    Correct, a fitting with an insulated throat would not require an additional (plastic) bushing by code.