    I agree the 'link' should occur in an accessible location. I just have to convince the client his idea is not a good one.
  2. #12
    Join Date
    Jun 2006
    Ohio
    Posts
    21,385
    Quote Originally Posted by Dale001289 View Post
    The sole connection to plant grounding system as required by 250.50 can result both common mode noise and objectionable currents. The removable link allows the field to 'trouble-shoot' the isolated grounding system and theoretically eliminate both.
    Mainly it's about common mode noise - not a loop
    All I see is someone looking for a reason to leave the EGS and the triad disconnected, i.e. completely isolate the equipment from the EGS. Doing so violates the listing for all equipment furnished with a ground prong or terminal.
    I will have achieved my life's goal if I die with a smile on my face.
  3. #13
    Join Date
    Apr 2016
    Georgia
    Posts
    489
    Smart-clientes love to do this . They hate the fact that a 'noisy, dirty' GES is connected to their precious DCS and PLC shields - i.e. isolated GES or Triad
    Unfortunately doing so is a violation of 250.50
  4. #14
    Join Date
    Feb 2009
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    9,563
    Dirt Worshipers can not be reasoned with.
    If you go and decide to dance with a gorilla the dance ain't over till the gorilla decides it's over.
  5. #15
    Join Date
    Apr 2016
    Georgia
    Posts
    489
    Agreed
  6. #16
    Join Date
    Feb 2003
    Fl
    Posts
    17,165
    Quote Originally Posted by ActionDave View Post
    Remember, a triad is in the shape of a cone foil hat and every-bit as effective.
    Roger
    Join Date
    Jun 2006
    Ohio
    Posts
    21,385
    It's a bleed over from one particular type of IEC grounding that is permitted. Tell them to get a backbone and do it the American way.
  8. #18
    Join Date
    Apr 2016
    Georgia
    Posts
    489
    Quote Originally Posted by Smart $ View Post
    I will do everything I can to convince them. The 'removable link' will be removed and will NEVER find its way home again.
  9. #19
    Join Date
    Aug 2004
    Northern illinois
    Posts
    16,785
    JMNSHO.
    If they have paid for this link, and it is code legal, you have an obligation to provide it unless they authorize its removal.
    Bob
  10. #20
    Join Date
    Jun 2006
    Ohio
    Posts
    21,385
    Quote Originally Posted by petersonra View Post
    JMNSHO.
    Using it to disconnect from the GES is noncompliant.... period.