    Enclosures

    The enclosure type that protects against incidental contact with the enclosed equipment; rain, snow, windblown dust; and hoedown is
    I put type NEMA 3x its wrong
    my question is how do i correctly ready table 110.28




  2. #2
    Join Date
    Feb 2003
    Location
    Seattle, WA
    Posts
    18,641
    Look for a column that has an X in each row associated with the conditions named in the question. Type 4 has an X in the incidental contact row, the rain and snow row, the dust row, and the hosedown row. That is the answer to this question.
    Charles E. Beck, P.E., Seattle
    Comments based on 2017 NEC unless otherwise noted.

  3. #3
    Join Date
    May 2017
    Location
    cudahy,California
    Posts
    16
    Makes prefect sense thanks for ur help