Results 1 to 3 of 3
Thread: Busbar rating
  1. #1
    Join Date
    Mar 2015
    Berkeley, CA
    Posts
    75
    Busbar rating
    Hi,
    Someone asked me this question the other day, and I wasn't quite sure how to answer it: If a panel says it is rated for 125A, is it just talking about the busbar portion of the panel? Or is it talking about the whole structural framework of the panel?
    Regards,
    Andy
  2. #2
    Join Date
    Jun 2004
    Cherry Valley NY, Seattle, WA
    Posts
    4,523
    Quote Originally Posted by andrew.tkelly View Post
    Hi,
    Regards,
    Andy
    I would say if it's a MLO panel, than it is the rating of the busbar. If it's a main breaker panel, that would be the rating of the main breaker, and the bus bar would be equal to or higher than that (usually the same). I'm sure there UL/ manufacturing standards for space for the cabinet that the panelboard is mounted in for a given amperage.
    Ethan Brush - East West Electric. NY, WA. MA
    "You can't generalize"
  3. #3
    Join Date
    Oct 2009
    Austin, TX, USA
    Posts
    9,800
    Hi,
    Regards,
    Andy
    It depends on the manufacturer. Some have separate stickers for the enclosure rating and for the "guts" of the panel rating, and sometimes they are different. You have to be careful; sometimes the enclosure sticker will say 225A but the bus is only 200A.
Posting Permissions
  • You may not post replies
  • You may not edit your posts