Thread: Electrical room Ground bus

  1. #1
    Join Date
    Apr 2008
    Posts
    100

    Electrical room Ground bus

    Continuous Ground bus in electrical room - can this be mounted at any height? There are obstructions upto 5' AFF.

  2. #2
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    23,538
    We mount them low or high sometimes even near the ceiling. The NEC is silent on this issue except to say that connections of the GEC must be accessible. {250.68(A)}
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted