Results 1 to 8 of 8
Thread: Tapping Riser
  1. #1
    Join Date
    Sep 2012
    NJ
    Posts
    2,029
    Tapping Riser
    Looking for a little help as I confused to the port quantity I would need. I’m tapping(2) sets to one. How does that work? If someone could give a little “idiotproof” walk thru of this. 2 existing phases get tapped to one? Thanks
    https://commerce.ilsco.com/e2wShoppi...183:3100012208
    Attached Images Attached Images
  2. #2
    Join Date
    Sep 2016
    Longmont, CO
    Posts
    182
    Sounds tricky, but maybe not. If you are physically cutting a new tap box into an existing riser, that may be a challenge in itself. You may need to support the vertical conductors that are below the box. I would recommend a mounted connection block with a cover, not the floating insulated variety your link took me to.
    https://commerce.ilsco.com/e2wShoppi...183:3100012318
    In order to accomplish this without replacing any of the conductors, it's going to be a challenge but not necessarily impossible. You must complete the parallel wiring on the existing sets of conductors, then tap each parallel connected set.
  3. #3
    Join Date
    Jul 2003
    New Jersey
    Posts
    25,380
    You'll need a 3 port Polaris or some other type of connector for three conductors. The #3 EGC with the tap conductors is likely too small.
    Rob
  4. #4
    Join Date
    Sep 2012
    NJ
    Posts
    2,029
    Quote Originally Posted by Jim1959 View Post
    Agreed. So in my mind this is what happens.
    1. Install new 3-1/2" pipe and wire to point near new splice box and new panel
    2. Shutdown power to existing feeders we are tapping.
    3. Cut existing riser conduits/feeders, support feeders.
    4. Cut in new splice box.
    5. Finish new 3-1/2" conduit install and splice/terminate.
    Sound right? Thanks.
  5. #5
    Join Date
    Sep 2016
    Longmont, CO
    Posts
    182
    Quote Originally Posted by infinity View Post
    If the existing is a parallel run, then a 5 port connector would be needed, right?
    2 in, 2 out and the tap.
  6. #6
    Join Date
    Sep 2016
    Longmont, CO
    Posts
    182
    Quote Originally Posted by mstrlucky74 View Post
    I think you are on the right track, I would allow for some adversity.............
  7. #7
    Join Date
    Jul 2003
    New Jersey
    Posts
    25,380
    Oops, yes you're correct, a 5 port is needed since the riser is continuing.
    Rob
  8. #8
    Join Date
    Jun 2006
    Ohio
    Posts
    21,385
    Need to know what's in EMDP-G5-42-MSB-2S1.
    One of these might work better: https://commerce.ilsco.com/e2wShoppi...237:3100012714
    I will have achieved my life's goal if I die with a smile on my face.
Posting Permissions
  • You may not post replies
  • You may not edit your posts