    Inverter on other side of a gate

    Hi,

    If I have a main panel separated from an inverter (maybe only 10 ft away from each other) by a gate, would I still need an AC disconnect, and therefore also a disconnect directory plaque? I'm not sure if the gate is locked or not.

    Regards,
    Andy

  2. #2
    Join Date
    May 2011
    Posts
    3,744
    I usually play that one safe and put in a disconnect. See the 'grouped' requirement in 690.15. Hard to argue that equipment on two sides of a gate is grouped.