    Hi, I saw some harmonics in a electric board so I would like to know what do you think.
    It my first time seeing this value 30% THD is a lot for me, but I have no enough experience to know if this is usual.
    Theory is different than experience.
    Enviado desde mi TA-1039 mediante Tapatalk
  2. #2
    Join Date
    Feb 2003
    New York, 40.7514,-73.9925
    Posts
    4,402
    What is the load as a percentage of the meter full scale? At load relative load, high THD is not a big deal.
    For example, if it was a 2000A meter and the load was 20A, a 30% THD is no big deal.
    If the load is relatively high, what is the load type and what harmonic makes up the biggest offender? lots of triplen harmonic?
    Ron
  3. #3
    Join Date
    Sep 2008
    UK
    Posts
    10,694
    Quote Originally Posted by KundaliniZero View Post
    Assuming the loads are single phase to neutral, 30% wouldn't altogether surprise me. Can you check the neutral?
  4. #4
    Join Date
    Feb 2013
    India
    Posts
    2,327
    Check THD for voltage also. What is it?