Page 2 of 4 FirstFirst 1234 LastLast
Results 11 to 20 of 32
Thread: Solid wire and crimping
  1. #11
    Join Date
    Dec 2013
    Kansas Cty, Mo, USA
    Posts
    478
    Quote Originally Posted by SceneryDriver View Post
    Funny you mention that. Last spring, I had to extend a Ufer connection to feed a new panel location. #4 wire fits a 3/16" oval copper Nicopress sleeve. Perfectly. Not a listed splice, but DEFINITELY irreversible and low resistance.
    I did this at my parents' house; I sleep just fine knowing how I did this splice.
    SceneryDriver
    heck yeah, I'd sleep okay with that
  2. #12
    Join Date
    Feb 2003
    Minnesota
    Posts
    6,830
    Quote Originally Posted by edward View Post
    Can solid wire (say #6 solid) be butt spliced using a crimped connection? I have never seen a solid wire crimped.
    T&B makes a line of C-Taps that are listed as Grounding and Bonding Equipment (suitable for splicing the GEC) that can be applied by T&B lever action crimpers. The T&B C-Tap #54720 will do two #6 solid copper conductors side-by-side. The #54720 is color coded "brown". The installation instructions are available Here.
    I picked up the tool, used, on eBay.
    Another Al in Minnesota
  3. #13
    Join Date
    Feb 2003
    Somewhere over the rainbow
    Posts
    3,279
    I know about the irreversable crimp option offered by NEC. But are the splices listed for SOLID conductor?
    ETA: just checked their site. Burndy YC4C6 are good for solid as well.
    Edward
    The only thing I know, is the progressive discovery of my ignorance
  4. #14
    Join Date
    Feb 2003
    San Jose, CA
    Posts
    1,502
    We use Ilsco C-Crimps that are listed for Solid CU.
    Curt Swartz
    Electrical Contractor
  5. #15
    Join Date
    May 2014
    AZ
    Posts
    2,325
    SceneryDriver
    care to explain
  6. #16
    Join Date
    Feb 2003
    Minnesota
    Posts
    6,830
    The T&B C-taps are listed for solid.
  7. #17
    Join Date
    Sep 2008
    UK
    Posts
    11,590
    Thank you.
    Copper is malleable so I guess it can be crimped. Even at #6AWG or around 16mm2 would be closest for us in the SI world........
    Not something I've tried...........
  8. #18
    Join Date
    Jul 2005
    LA basin, CA
    Posts
    1,808
    Quote Originally Posted by FionaZuppa View Post
    care to explain
    Good Eye Fiona
    Could that be carrying neutral current thru water pipes?
    Caused by open service neutral?
    Roger Ramjet NoFixNoPay
  9. #19
    Join Date
    Jul 2007
    Clark County, NV
    Posts
    1,098
    I thought that looked funny but didn't blow it up to look at it further. I figured he HAD to have known about it, and didn't share, so it must have been a non-issue. But, well, it sure LOOKS LIKE an issue!
  10. #20
    Join Date
    Jun 2003
    NE (9.1 miles @5.07 Degrees from Winged Horses)
    Posts
    9,712
    Looks like a metal raceway enclosing an GEC that was not properly bonded to it at either end. Perhaps a shot of lightning at some time or another, proving a picture is worth a thousand words.
    Personally, I would not bother with putting that type of splice in a box nor would it V.
    Tom
    TBLO
Posting Permissions
  • You may not post replies
  • You may not edit your posts