    Solid wire and crimping

    Can solid wire (say #6 solid) be butt spliced using a crimped connection? I have never seen a solid wire crimped.

    Thank you.
    Edward
    The only thing I know, is the progressive discovery of my ignorance


  2. #2
    Join Date
    Dec 2012
    Location
    Placerville, CA, USA
    Posts
    18,177
    Quote Originally Posted by edward View Post
    Can solid wire (say #6 solid) be butt spliced using a crimped connection? I have never seen a solid wire crimped.

    Thank you.
    Some but by no means all butt splice connectors are rated for solid wire. I would expect to have to use a cycle controlled crimper to match the connectors. No universal crimp pliers if using solid wire.
    JMO

  3. #3
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    23,560
    Just curious, who uses #6 solid and why?
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  4. #4
    Join Date
    Jul 2007
    Location
    Clark County, NV
    Posts
    186
    Quote Originally Posted by infinity View Post
    Just curious, who uses #6 solid and why?
    Grounding of panels and other required equipment.

    Can't think where I've ever seen it spliced though.

  5. #5
    Join Date
    Feb 2003
    Location
    Somewhere over the rainbow
    Posts
    3,198
    It is for GEC extension.

    The plumbers did a plumbing upgrade and the city has required a new grounding system. The plumbers did not do the GEC properly so the customer wants me to use a butt splice to extend the GEC to the panel and I refused to use a crimp and butt splice on the solid wire.

    I said I will replace the whole system properly without a butt splice.
    Edward
    The only thing I know, is the progressive discovery of my ignorance


  6. #6
    Join Date
    Jun 2003
    Location
    NE (9.1 miles @5.07 Degrees from Winged Horses)
    Posts
    8,760
    Quote Originally Posted by edward View Post
    It is for GEC extension.

    The plumbers did a plumbing upgrade and the city has required a new grounding system. The plumbers did not do the GEC properly so the customer wants me to use a butt splice to extend the GEC to the panel and I refused to use a crimp and butt splice on the solid wire.

    I said I will replace the whole system properly without a butt splice.
    Cadweld or similar should be adequate but may be more expensive than the new 6.
    Tom
    TBLO

  7. #7
    Join Date
    Feb 2009
    Location
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    8,623
    Quote Originally Posted by edward View Post
    It is for GEC extension.

    The plumbers did a plumbing upgrade and the city has required a new grounding system. The plumbers did not do the GEC properly so the customer wants me to use a butt splice to extend the GEC to the panel and I refused to use a crimp and butt splice on the solid wire.

    I said I will replace the whole system properly without a butt splice.
    Irreversible crimp is all you need.
    Once in a while you get shown the light
    In the strangest of places if you look at it right. Robert Hunter

  8. #8
    Join Date
    Jun 2003
    Location
    NE (9.1 miles @5.07 Degrees from Winged Horses)
    Posts
    8,760
    Quote Originally Posted by ActionDave View Post
    Irreversible crimp is all you need.
    Burndy YC4C6 less than $6 if you have the tool or can borrow one.
    Tom
    TBLO

  9. #9
    Join Date
    Dec 2013
    Location
    Kansas Cty, Mo, USA
    Posts
    454
    Don't call me stupid, but I've wondered about using a swaging tool and aluminum crimp sleeves. The kind you would use for wire rope or Airline cable.

    Never done it, but I thought about it in the past

  10. #10
    Join Date
    Aug 2013
    Location
    New York, NY
    Posts
    396
    Quote Originally Posted by James L View Post
    Don't call me stupid, but I've wondered about using a swaging tool and aluminum crimp sleeves. The kind you would use for wire rope or Airline cable.

    Never done it, but I thought about it in the past
    Funny you mention that. Last spring, I had to extend a Ufer connection to feed a new panel location. #4 wire fits a 3/16" oval copper Nicopress sleeve. Perfectly. Not a listed splice, but DEFINITELY irreversible and low resistance.

    Name:  IMG_2550.jpg
Views: 308
Size:  144.4 KB

    I did this at my parents' house; I sleep just fine knowing how I did this splice.