Thread: Standard VFD and transformer sizing practices?

  1. #1
    Join Date
    Oct 2017
    Location
    CA
    Posts
    11

    Standard VFD and transformer sizing practices?

    What I have here is one of our 100 hp VFD's went out. Currently it is powering a 108 hp motor. I would like to get a larger VFD for this configuration but it is on a 125kva transformer.

    My question here is what is the standard practice in sizing the two? I'm sure there is nothing wrong with having a larger transformer than the VFD, but is there anything wrong with having a larger VFD than transformer? I am thinking that I can just set the overloads on the VFD at around 150A but always think that the next guy in there can raise it up some time down the road for what ever reason and blow the transformer if the pump and motor gets stuck.

    So is it standard to just size the transformer larger than the drive?

    Here is how the power goes:

    480V MCC > 100 hp VFD > 125kva isolation step up transformer > 108 hp, 1775v, 39A motor.

    Transformer ratio 1910/480= 3.98* 39A= 155A@ 480v* 120%= 186A

  2. #2
    Join Date
    Jan 2016
    Location
    PA
    Posts
    4,174
    Weird voltages
    motor 1775
    xfmr 1910

    For this application I would size the xfmr based on vfd output v and i
    Assume 125 A at 480 vac, kva = 104 kva
    a 125 kva should be fine

    what is the actual motor voltage
    assume 3.98 x 480 ~ 1910
    kva at 39 A = 129 kva
    but since v is higher than rated i should be lower
    xfmr is marginal



  3. #3
    Join Date
    Oct 2017
    Location
    CA
    Posts
    11
    Quote Originally Posted by Ingenieur View Post
    Weird voltages
    motor 1775
    xfmr 1910

    For this application I would size the xfmr based on vfd output v and i
    Assume 125 A at 480 vac, kva = 104 kva
    a 125 kva should be fine

    what is the actual motor voltage
    assume 3.98 x 480 ~ 1910
    kva at 39 A = 129 kva
    but since v is higher than rated i should be lower
    xfmr is marginal
    The motor voltage is 1775v, but I don't know what the actual voltage is by the time it reaches the motor since it isn't accessible.

    We plan to keep the existing 125kva xfmr, at least until it fails. And also keep the motor but I would like a larger drive. The question i'm wondering is should the drive always be smaller than the transformer?

  4. #4
    Join Date
    Jul 2006
    Location
    San Francisco, CA, USA
    Posts
    7,028
    1775V? Never heard of it. I'm more inclined to believe that 1775 is the RPM, the transformer is likely just a 1:1 Delta-Wye drive isolation transformer because the 480V source is Delta and the VFD mfr required Wye. But hey, I'm not there to look at it, I'm just going by the fact that 1775V would be classified as Medium Voltage and would require a MUCH different VFD that would NOT be anywhere near 'standard" in any way, shape or form.

    A 100HP 125A output VFD will have an input of around 97.6kVA (pulling this off of an Allen Bradley VFD chart). So if that transformer is used ONLY for that drive, it's fine. Sizing a transformer that close to the VFD size WILL increase the harmonic distortion quite a bit though, so hopefully that transformer is not feeding anything else.

    Unless... the transformer is on the OUTPUT side of the VFD and the motor is on something like a deep sea submersible robot, using a custom wound motor because of the extreme voltage drop on a miles-long cable. In that case, that transformer may be too small.

    Oh wait, I just read your post again, that's exactly what you said. Sorry...
    The transformer will end up absorbing a lot of the output harmonics and if operated at less than design frequency, will experience added eddy current heating in the core. The usualy practice is to either design the transformer with a special core, or over size it by 50%.
    Last edited by Jraef; 10-06-17 at 11:21 PM.
    __________________________________________________ ____________________________
    Many people are shocked when they discover I am not a good electrician...

  5. #5
    Join Date
    Oct 2017
    Location
    CA
    Posts
    11
    Quote Originally Posted by Jraef View Post
    1775V? Never heard of it. I'm more inclined to believe that 1775 is the RPM, the transformer is likely just a 1:1 Delta-Wye drive isolation transformer because the 480V source is Delta and the VFD mfr required Wye. But hey, I'm not there to look at it, I'm just going by the fact that 1775V would be classified as Medium Voltage and would require a MUCH different VFD that would NOT be anywhere near 'standard" in any way, shape or form.

    A 100HP 125A output VFD will have an input of around 97.6kVA (pulling this off of an Allen Bradley VFD chart). So if that transformer is used ONLY for that drive, it's fine. Sizing a transformer that close to the VFD size WILL increase the harmonic distortion quite a bit though, so hopefully that transformer is not feeding anything else.
    It is a step up isolation transformer. The motor is 1775v, 3470 RPM.
    The vfd is only 480v, which powers the step up xfmr, which powers the motor.

    The transformer is only used to power just this 1 motor, nothing else. I know the motor and transformer combination isn't ideal but its what I have to work with on this one.

  6. #6
    Join Date
    Oct 2017
    Location
    CA
    Posts
    11
    Quote Originally Posted by Jraef View Post
    Unless... the transformer is on the OUTPUT side of the VFD and the motor is on something like a deep sea submersible robot, using a custom wound motor because of the extreme voltage drop on a miles-long cable. In that case, that transformer may be too small.

    Oh wait, I just read your post again, that's exactly what you said. Sorry...
    The transformer will end up absorbing a lot of the output harmonics and if operated at less than design frequency, will experience added eddy current heating in the core. The usualy practice is to either design the transformer with a special core, or over size it by 50%.
    Yep, the motor is under the ocean floor with a pump on it.

    Over size the transformer by 50% of the motor is standard? What about sizing the drive? Just keep it smaller than the transformer does anyone go larger drive than transformer?

  7. #7
    Join Date
    Jan 2016
    Location
    PA
    Posts
    4,174
    Is the motor actually operating at 100% load?
    often it is less, 80-90%

    how is the speed modulated?
    continuously by a pid?
    constant speed?
    etc



  8. #8
    Join Date
    Sep 2008
    Location
    UK
    Posts
    10,355
    Quote Originally Posted by paul_arc View Post
    What I have here is one of our 100 hp VFD's went out. Currently it is powering a 108 hp motor. I would like to get a larger VFD for this configuration but it is on a 125kva transformer.

    My question here is what is the standard practice in sizing the two? I'm sure there is nothing wrong with having a larger transformer than the VFD, but is there anything wrong with having a larger VFD than transformer? I am thinking that I can just set the overloads on the VFD at around 150A but always think that the next guy in there can raise it up some time down the road for what ever reason and blow the transformer if the pump and motor gets stuck.

    So is it standard to just size the transformer larger than the drive?

    Here is how the power goes:

    480V MCC > 100 hp VFD > 125kva isolation step up transformer > 108 hp, 1775v, 39A motor.

    Transformer ratio 1910/480= 3.98* 39A= 155A@ 480v* 120%= 186A
    A couple of points if I may?
    You can't use the motor current to calculate the VSD input kVA. The input power factor is usually significantly higher than the motor power factor.
    Powering a step up transformer from a VFD needs special considerations. Any asymmetrical component in the drive PWM output can cause transformer saturation.
    I have done a few VFDs with a transformer on the output but they were custom built with an air gap in the core. Just be aware that this is not for the faint hearted.
    Si hoc legere scis nimium eruditionis habes.

  9. #9
    Join Date
    Jul 2006
    Location
    San Francisco, CA, USA
    Posts
    7,028
    Quote Originally Posted by paul_arc View Post
    Yep, the motor is under the ocean floor with a pump on it.

    Over size the transformer by 50% of the motor is standard? What about sizing the drive? Just keep it smaller than the transformer does anyone go larger drive than transformer?
    Over sizing by 50% is a "poor man's" work around to the problem of the complexity of running a motor through a transformer on the load side of a VFD rather than spend the money (and lead time) to have a custom transformer built to handle it properly. Besoeker's mention of building it with a special air gap is a common solution, I've seen others, but none of them cheap or fast.

    The problem from the VFD's standpoint is that the drive must be sized not only for the motor, but also for the losses between the drive and the load, which will now include the transformer and cable losses. So "fudging it" by over sizing the transformer to handle the added heat means paying for it in the VFD sizing anyway.

    In your case you already have this transformer and for all we know, it was custom made for this application, I mean it's not as though a bizarre ratio like that exists off the shelf somewhere anyway. So assuming someone knew what they were doing with that, and assuming that part of it was working fine, to my mind all you need do is increase the size of the VFD. The fact that the first one eventually failed was possibly related to it being constantly operated at maximum capacity. Over sizing would be almost imperative in this situation. Over sizing a VFD for an application hurts nothing but the budget, up to a point. Many VFDs will not like being connected to a load smaller than 50% of its rating just because of sensor range tolerance issues. So I would not go larger than a 200HP drive. But how big, I don't know.

    If you have any empirical data on how the last drive was operating, than might be helpful in deciding, but if it was in a constant state of current limit at its maximum output, you may not know what it could have seen if it were possible to operate at full speed. But one possible indirect (albeit crude) way of estimating would be that if for example it was in a constant state of current limit at 125A, and to achieve that the output frequency was limited to, let's say 48Hz, that's 80% speed. If it's a simpler constant torque load, like it would be with a positive displacement pump, you can simply see it as a 125% increase (the inverse of 80%) in power (kW) to get 100% speed from it. If the load is a centrifugal (aka quadratic) pump it gets a little more complicated as to the load at 100% speed because the power requirement will increase at the cube of the speed change, so 195% power would be inferred (125% cubed). Then from whatever power increase you see, to get the drive output current required you will have to know (or reasonably guess) the power factor of the motor at those speeds.

    Yours is not a simple challenge to be sure...
    __________________________________________________ ____________________________
    Many people are shocked when they discover I am not a good electrician...

  10. #10
    Join Date
    Feb 2012
    Location
    United States
    Posts
    588
    I agree that you can put in a larger VFD so it does not have to work as hard and should then last longer than the last one did (how long DID it last?).

    We typically use an AUTO transformer rather than iso - get same output voltage conversion, added L filtering, and non of the additional transformer heating due to running at lower than its design frequency; but in our uses, we typically need to run from about 10hz to 100hz. Use them for both increase and decrease output voltages for various reasons. Not as common as it used to be though. All were designed for the application, or oversized if standard transformers as Jraef stated. Easy analogy for oversizing: is you would not expect a 60hz transformer to run loaded at 50hz, let alone the added harmonic load.

    Since yours is a pump, I agree you probably run at near base speed; and as commented previously, the transformer still works fine. I doubt you would run a new 25-50% oversized VFD at higher load than present. If it made you feel better, slide thermal switches between core and each coil, put them in series, and feed to your control or VFD to shut down if it gets too hot. Then just move on to the next project.