    Quote Originally Posted by infinity View Post
    With the number of conductors required for either scenario, then no. Just ensure that the box is the proper size.
    ty
  2. #12
    Join Date
    Sep 2012
    NJ
    Posts
    2,015
    How about if this was MC cable and not conduit? Same circuit or 3 diff circuits. Would this be any different? Thanks.
  3. #13
    Join Date
    Jul 2003
    New Jersey
    Posts
    25,196
    Quote Originally Posted by mstrlucky74 View Post
    Since you have separate neutrals then use a single 12-2 MC cable for each circuit.
    Rob
  4. #14
    Join Date
    Jul 2007
    Clark County, NV
    Posts
    1,098
    I must have missed which one this is. And were the separate neutrals required?
    If this is 3-phase, you could use a single 12/4 cable to the first box, right? 12/3 to the second, 12/2 to the third...
    If this is single-phase, would a 12/4 "super-neutral" be allowed to the first box? It's been a long time since I used that.
  5. #15
    Join Date
    Jul 2003
    New Jersey
    Posts
    25,196
    Quote Originally Posted by MAC702 View Post
    Looking back I believe that you're correct I don't see a requirement in MstrLuckys post to suggest that there must be separate neutrals.
    Rob
  6. #16
    Join Date
    Sep 2012
    NJ
    Posts
    2,015
    Sorry, yes separate neutrals are required. But there are multiple neutral MC cables.
  7. #17
    Join Date
    Jul 2003
    New Jersey
    Posts
    25,196
    Whew, OK then everything that I've said so far is still applicable to your installation.