I am thinking of using USE wire for a service lateral, installed in PVC schedule 80 conduit. I could get by with XHHW in the conduit, but the USE is more durable. Why is there (apparently) no listing in the code conduit fill charts for USE? If there is, I can't find it. Thanks for the help.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
See note #5 in the "Notes to Tables" in Chapter 9

Roger
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
USE is generally listed as Rhw-2. At least the newer stuff seems to be that way. All the mobile home cable is also listed that way
 