    wire fill

    how many #10 thhn wires can I put in 3/4" thinwall
    Let's pray that the human race never escapes Earth to spread it's ineiquity eleswhere. C.S. Lewis

  2. #2
    Join Date
    Jul 2005
    Location
    Tennessee
    Posts
    15,383
    lost your Code book ?
    according to Table C1.. 10
    (unless it's less than 24")
    At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.

  3. #3
    Join Date
    Feb 2003
    Location
    Bremerton, Washington
    Posts
    7,606
    There is a difference between what the code allows and what is possible
    Moderator-Washington State
    Ancora Imparo

  4. #4
    Join Date
    May 2013
    Location
    Massachusetts
    Posts
    2,234
    Quote Originally Posted by tom baker View Post
    There is a difference between what the code allows and what is possible
    How do you quantify what is actually possible to do?

    I've heard this numerous times before that the NEC conduit sizing is more ambitious than how one really should expect to build it in the field. But how does a person calculate what to specify, so that what gets specified is practical to build?

  5. #5
    Join Date
    Feb 2009
    Location
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    8,623
    Quote Originally Posted by tom baker View Post
    There is a difference between what the code allows and what is possible
    Quote Originally Posted by Carultch View Post
    How do you quantify what is actually possible to do?

    I've heard this numerous times before that the NEC conduit sizing is more ambitious than how one really should expect to build it in the field. But how does a person calculate what to specify, so that what gets specified is practical to build?
    If you know how to do the work smartly pulling all 40% that the code allows is not hard for smaller wire gauges. When you get into 300MCM and up it's worth thinking about upsizing the conduit some.
    Once in a while you get shown the light