Thread: Garage and outside receptacles

  1. #11
    Join Date
    Apr 2003
    Location
    Fort Collins, Colorado
    Posts
    1,556
    2017 NEC 210.11(C)(4) exception allows it as long as the receptacle is readily accessible.
    Ron

  2. #12
    Join Date
    Jul 2005
    Location
    LA basin, CA
    Posts
    1,542
    Quote Originally Posted by rcarroll View Post
    2017 NEC 210.11(C)(4) exception allows it as long as the receptacle is readily accessible.
    MWBCs feeding a garage sub-panel, may also satisfy the dedicated branch circuit, outside circuits, and Energy Code / Green Codes for Car-charging raceways.
    Roger Ramjet NoFixNoPay

  3. #13
    Join Date
    Feb 2003
    Location
    Somewhere over the rainbow
    Posts
    3,200
    As stated earlier, it is allowed to have the indoor receptacle also power the outdoor receptacle. 210.11(C)(4) new section for the 2017 NEC
    Edward
    The only thing I know, is the progressive discovery of my ignorance


  4. #14
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    23,566
    Quote Originally Posted by edward View Post
    As stated earlier, it is allowed to have the indoor receptacle also power the outdoor receptacle. 210.11(C)(4) new section for the 2017 NEC
    Yes, my earlier post said the 2017 when it should have said 2014. The 2017 added the exception that
    Ron first mentioned.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  5. #15
    Join Date
    Jun 2012
    Location
    NW Ohio
    Posts
    892
    Although it would be nice if 210.52(g)(1) would refer to the circuit requirement and exception found at 210.11(c)(4)

  6. #16
    Join Date
    Jun 2017
    Location
    Burkburnett,tx
    Posts
    21
    Quote Originally Posted by mopowr steve View Post
    Although it would be nice if 210.52(g)(1) would refer to the circuit requirement and exception found at 210.11(c)(4)
    Agreed


    Sent from my iPhone using Tapatalk

  7. #17
    Join Date
    Jan 2007
    Posts
    2,850
    Quote Originally Posted by ramsy View Post
    MWBCs feeding a garage sub-panel, may also satisfy the dedicated branch circuit, outside circuits, and Energy Code / Green Codes for Car-charging raceways.
    I'd have to say that a MWBC feeding a garage sub-panel would actually be considered a feeder.


    JAP>

  8. #18
    Join Date
    Oct 2017
    Location
    Tyler, TX, USA
    Posts
    2

    210.11(C)(4) Exception

    I believe the 2017 NEC permits "readily accessible outdoor receptacle outlets for the garage circuit in the Exception to 210.11(C)(4).

  9. #19
    Join Date
    Jul 2005
    Location
    LA basin, CA
    Posts
    1,542
    Roger that, especially if exceeding 20 Amps
    Roger Ramjet NoFixNoPay

  10. #20
    Join Date
    Feb 2003
    Location
    Bremerton, Washington
    Posts
    7,610
    There is an exception for readily accessible receptacles in that new section take a look at that
    Moderator-Washington State