Thread: Garage and outside receptacles

  1. #21
    Join Date
    Jun 2013
    Location
    Massachusetts
    Posts
    26
    Quote Originally Posted by infinity View Post
    Under the 2017 you cannot put an outside receptacle on with the garage receptacles.

    If the outside receptacle is readily accessible then you can have it on the circuit that feeds the garage, 210-11 (C)(4) exception. 2017 code cycle

  2. #22
    Join Date
    Apr 2003
    Location
    Fort Collins, Colorado
    Posts
    1,556
    Quote Originally Posted by lordofthisworld View Post
    If the outside receptacle is readily accessible then you can have it on the circuit that feeds the garage, 210-11 (C)(4) exception. 2017 code cycle
    This is new for the 2017 code. Infinity is correct under the 2014 NEC.
    Ron