Thread: 5 homes burn after POCO connects power after hurricane

  1. #11
    Join Date
    Jul 2005
    Location
    LA basin, CA
    Posts
    1,537
    Quote Originally Posted by Ingenieur View Post
    ..how would i flow with no neutral?
    1) Telephone & cable, bonded to PoCo ground, carry open-neutral current back to service-neutral via building main bonding.
    This un-fused structured cable is not designed to carry building power, and doing so with open neutrals can ignite buildings.

    2) Water/gas lines, and re-enforced concrete provide neutral return paths to PoCo thru Main bonding and earth, but are less a fire hazard than
    a shock hazard to plumbers, and expendable laborers, if contained without legal recourse against unauthorized or unqualified access to building services.
    Roger Ramjet NoFixNoPay

  2. #12
    Join Date
    Jul 2005
    Location
    LA basin, CA
    Posts
    1,537
    Quote Originally Posted by Ingenieur View Post
    I suppose you could get 240 across 120'devices
    Multi-wire branch circuits (MWBC) share the same neutral to get multiple L-N circuits on different phase conductors.

    A completely open-service return prohibits L-N voltage, but shared neutrals find higher-Z Line-Line paths thru appliance loads. Although listed appliances are destructively tested to fail harmlessly open, long before they catch fire.

    Some high-voltage distribution systems use "Single Wire Earth Return" (SWER), including the Los Angeles Dpt. of Water & Power at 5.8kv. If high-voltage systems can feed multiple transformers, the same way MWBC's feed L-N outlets on different phase conductors, then an open-ground at distribution voltage can find a higher-Z Line-Line path thru buildings.

    The 5 homes that burned in Florida may not be related to inside wiring, if the PoCo fired up a transformer without a line-side ground connection.
    Last edited by ramsy; 10-10-17 at 12:50 AM.
    Roger Ramjet NoFixNoPay

  3. #13
    Join Date
    Jul 2005
    Location
    LA basin, CA
    Posts
    1,537
    Edit time expired:
    "The 5 homes that burned in Florida may not be related to inside wiring, if the PoCo fired up a transformer without a primary ground connection."
    Roger Ramjet NoFixNoPay

  4. #14
    Join Date
    Dec 2011
    Location
    Ocala, Florida, USA
    Posts
    2,300
    Quote Originally Posted by GoldDigger View Post
    But a lost/unconnected neutral can send enough current through a powered on device to cause it to burn. For a small to medium load this would not even need to draw a maximum current from the branch circuit, let alone enough to blow a breaker.

    The only protection against that is to make sure the main is open at all connected buildings before energizing the service transformer.

    Sent from my XT1585 using Tapatalk

    But for it to happen to five houses on the same transformer?


    I know what I don't know, and I know where to go to find it!

  5. #15
    Join Date
    Feb 2003
    Location
    Somewhere over the rainbow
    Posts
    3,195
    Quote Originally Posted by ramsy View Post

    Some high-voltage distribution systems use "Single Wire Earth Return" (SWER), including the Los Angeles Dpt. of Water & Power at 5.8kv. If high-voltage systems can feed multiple transformers, the same way MWBC's feed L-N outlets on different phase conductors, then an open-ground at distribution voltage can find a higher-Z Line-Line path thru buildings.

    The 5 homes that burned in Florida may not be related to inside wiring, if the PoCo fired up a transformer without a line-side ground connection.
    So a SWER works the same concept as our basic MWBC but utility higher voltage uses the earth as the grounded conductor?
    Edward
    The only thing I know, is the progressive discovery of my ignorance


  6. #16
    Join Date
    Jul 2005
    Location
    LA basin, CA
    Posts
    1,537
    Quote Originally Posted by edward View Post
    So a SWER works the same concept as our basic MWBC but utility higher voltage uses the earth as the grounded conductor?
    Larger SWER systems with 2 or 3 legs of phase conductors may be similar to our basic MWBC, but perhaps not with a single leg.

    Seems to me any distribution system using a primary ground to divide voltage, which can break open, offers primary voltage to any connected secondary grounds or buildings offering a return path, which is different from a shorted transformer.
    Last edited by ramsy; 10-10-17 at 12:53 PM.
    Roger Ramjet NoFixNoPay

  7. #17
    Join Date
    Sep 2016
    Location
    Longmont, CO
    Posts
    167
    Quote Originally Posted by edward View Post
    Hence the reason our POCO (PG&E) will not turn ON the main breaker and will not even energize the meter if the reading are not correct at the meter jaw.
    This can however be deceiving, the voltage may read fine without a load, but if there is a neutral issue, it won't become apparent until the system is loaded.

  8. #18
    Join Date
    Nov 2007
    Posts
    781
    Quote Originally Posted by Jim1959 View Post
    This can however be deceiving, the voltage may read fine without a load, but if there is a neutral issue, it won't become apparent until the system is loaded.
    If that's the case, the PoCo has nothing to do with the incident. Anything beyond the service meter is HO's responsibility.

  9. #19
    Join Date
    Dec 2012
    Location
    Placerville, CA, USA
    Posts
    18,169
    Quote Originally Posted by topgone View Post
    If that's the case, the PoCo has nothing to do with the incident. Anything beyond the service meter is HO's responsibility.
    Note that we said that is might read fine at the meter, not that it was fine at the meter. If the POCO neutral is missing between transformer and service point, any resulting damage is their responsibility. If the neutral problem is downstream of the service point, then the HO may be on the hook, although it would mean that POCO restored service to a damaged building wiring system.

  10. #20
    Join Date
    Jan 2014
    Location
    chicago, il, USA
    Posts
    335
    I wonder if someone mixed up a hot with the grounded conductor. I find it hard to believe that 5 separate structures caught fire because of an open neutral.