Thread: Reactance value in Voltage drop calculations

  1. #1
    Join Date
    Apr 2013
    Location
    Riyadh,KSA
    Posts
    60

    Reactance value in Voltage drop calculations

    There is one case we face in our project and I ask for your support.
    the case is for voltage drop cal. for cable size 300 or 400 mm2 the current is 306 A, AC and the distance is 350 meter. The issue is the end user representative want to consider the reactance value for that cable for VD but I neglect this value and take the resistance only.
    Any one can tell me what is the right to consider or to neglect.

  2. #2
    Join Date
    Jun 2006
    Location
    Ohio
    Posts
    21,385
    On an engineering level, consider. At 400mm², the reactance can be more than double the resistance.
    I will have achieved my life's goal if I die with a smile on my face.

  3. #3
    Join Date
    Apr 2013
    Location
    Riyadh,KSA
    Posts
    60
    Quote Originally Posted by Smart $ View Post
    On an engineering level, consider. At 400mm², the reactance can be more than double the resistance.
    Thanks.