    Article 600.5 (A) Sign circuit

    Does each sign require it's own sign circuit? My interpretation is that each building must have at least one dedicated 20A circuit, but that could be for multiple signs up to the allowable ampacity 16A. I had a sign guy ask me to quote a home run, saying it was against code to use the same circuit.

  2. #2
    Join Date
    Jun 2003
    Posts
    6,760
    I would agree with you. One circuit, as many signs as desired up to the 16 amps.