Outside feeder roundung up

Status
Not open for further replies.

Caligula

Member
Service entrance OCPD's cannot be rounded up when protecting service entrance conductors.

An outside feeder to another building on site must terminate at a disconnecting means just like a service....but is not a service entrance.

If that feeder terminates into an OCPD can it be rounded up like a typical circuit or must the situation be treated like a service entrance?
 
I think you are mixing things up a bit: note that the OCPD at the "end" of the feeder does no have to be coordinated with the feeder ampacity - the feeder is protected by the OCPD on its SUPPLY SIDE. You dont need overcurrent protection at all at the remote building, just a disconnecting means (the exception would be if the feeder was a tap per 240.21(B)(5), then you do and you cant use "next size up", or if you needed to protect a panelboard per 408.36)
 