    How many of these drivers could I put on a 120v circuit or would be a practical design? It says 5-40w driver? How would I calculate that per 120v 20a circuit. About 1 amp per 100watts? Watts to amps? Thanks,
    http://www.lutron.com/TechnicalDocum...40_LED_4.8.pdf
  2. #2
    Join Date
    Feb 2003
    Bremerton, Washington
    Posts
    7,934
    Input is .51A. Do the math....
    Moderator-Washington State
    Ancora Imparo
  3. #3
    Join Date
    Sep 2012
    NJ
    Posts
    2,159
    Quote Originally Posted by tom baker View Post
    Ok Im not 100% clear. Your taking that pic from the pic of the ballast correct? So would I say ok 80% of 20A and divide that by .51? SO about 33 fixtures on 1 20A circuit? Seems like a lot.
  4. #4
    Join Date
    Jul 2003
    New Jersey
    Posts
    25,863
    As Tom stated the driver input current is .51 amps @120 volts so forget the watts/amps. Your calculation appears correct.
    Rob
    All responses based on the 2014 NEC unless otherwise noted
  5. #5
    Join Date
    Jul 2007
    Clark County, NV
    Posts
    1,106
    Quote Originally Posted by mstrlucky74 View Post
    ...Seems like a lot.
    Welcome to the LED world!
  6. #6
    Join Date
    Sep 2012
    NJ
    Posts
    2,159
    Quote Originally Posted by infinity View Post
    Thanks
  7. #7
    Join Date
    Sep 2012
    NJ
    Posts
    2,159
    Quote Originally Posted by MAC702 View Post
    lol.
  8. #8
    Join Date
    Jul 2003
    New Jersey
    Posts
    25,863
    I checked your numbers and get 31 drivers.
    20 amps * 80% = 16 amps
    31*.51 amps = 15.8 amps
    Rob
  9. #9
    Join Date
    Sep 2012
    NJ
    Posts
    2,159
    TY
  10. #10
    Join Date
    Apr 2008
    Ann Arbor, Michigan
    Posts
    6,981
    171011-1256 EDT
    You really need to know more about the driver to determine if it is advisable to put that many on the circuit.