    Grounding and bonding/ electrically continuously

    I need to bond this piece of flex to the cable tray with out removing the flex, does anyone have an idea or a UL listed fitting other than the regular connector with an exterior lug. The white bushing is not UL listed for that purpose, thats for rigid conduit.


    Sent from my iPhone using Tapatalk

  2. #2
    Join Date
    Feb 2003
    Location
    Minnesota
    Posts
    6,512
    There are split grounding bushings available.

    Another Al in Minnesota

  3. #3
    Join Date
    May 2003
    Location
    Leesburg, VA
    Posts
    7,023
    What is the white bushing; plastic?
    Brian John
    Leesburg, VA

  4. #4
    Join Date
    May 2017
    Location
    Yuma Az united States
    Posts
    46
    Quote Originally Posted by al hildenbrand View Post
    There are split grounding bushings available.

    I like that one and i have seen it on garvin supplies, can it be use on liquid tight flex


    Sent from my iPhone using Tapatalk

  5. #5
    Join Date
    May 2003
    Location
    Leesburg, VA
    Posts
    7,023
    Is there a connector on the liquidtite?

    Is there an EGC in the liquidtite
    Brian John
    Leesburg, VA

  6. #6
    Join Date
    Feb 2003
    Location
    Fl
    Posts
    16,627
    Quote Originally Posted by brian john View Post
    Is there a connector on the liquidtite?

    Is there an EGC in the liquidtite
    I second Brian's questions

    Roger
    Moderator

  7. #7
    Join Date
    Jan 2014
    Location
    chicago, il, USA
    Posts
    335
    Would it meet code if he bonded the cabinet where the flex terminates to the cable tray?
    The world is round, you will get there no matter what path you take.

  8. #8
    Join Date
    Feb 2009
    Location
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    8,623
    Quote Originally Posted by rlundsrud View Post
    Would it meet code if he bonded the cabinet where the flex terminates to the cable tray?
    We can't tell what's going on in the picture. It may meet code already. Adding a grounding bushing may not do anything even if the desire is to go above code. Until the questions Brian John asked are answered we won't know what to recommend.
    Once in a while you get shown the light
    In the strangest of places if you look at it right. Robert Hunter