Results 1 to 8 of 8
Thread: Grounding and bonding/ electrically continuously
  1. #1
    Join Date
    May 2017
    Yuma Az united States
    Posts
    51
    I need to bond this piece of flex to the cable tray with out removing the flex, does anyone have an idea or a UL listed fitting other than the regular connector with an exterior lug. The white bushing is not UL listed for that purpose, thats for rigid conduit.
  2. #2
    Join Date
    Feb 2003
    Minnesota
    Posts
    6,797
    There are split grounding bushings available.
    Another Al in Minnesota
  3. #3
    Join Date
    May 2003
    Leesburg, VA
    Posts
    7,072
    What is the white bushing; plastic?
    Brian John
    Leesburg, VA
  4. #4
    Join Date
    May 2017
    Posts
    51
    Quote Originally Posted by al hildenbrand View Post
    I like that one and i have seen it on garvin supplies, can it be use on liquid tight flex
  5. #5
    Join Date
    May 2003
    Leesburg, VA
    Posts
    7,072
    Is there a connector on the liquidtite?
    Is there an EGC in the liquidtite
    Brian John
    Leesburg, VA
  6. #6
    Join Date
    Feb 2003
    Fl
    Posts
    17,165
    Quote Originally Posted by brian john View Post
    I second Brian's questions
    Roger
    Join Date
    Jan 2014
    chicago, il, USA
    Posts
    393
    Would it meet code if he bonded the cabinet where the flex terminates to the cable tray?
    The world is round, you will get there no matter what path you take.
  8. #8
    Join Date
    Feb 2009
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    9,563
    Quote Originally Posted by rlundsrud View Post
    We can't tell what's going on in the picture. It may meet code already. Adding a grounding bushing may not do anything even if the desire is to go above code. Until the questions Brian John asked are answered we won't know what to recommend.
    If you go and decide to dance with a gorilla the dance ain't over till the gorilla decides it's over.