    Grounding bushings
    Are grounding bushings required on flexible conduit connectors?
  2. #2
    Join Date
    Jul 2007
    Clark County, NV
    Posts
    1,098
    What voltage? Amperage? Length of conduit? Which type of connector; clamp? Installed in eccentric or concentric KOs?
  3. #3
    Join Date
    Jul 2003
    New Jersey
    Posts
    25,380
    Depends on the size and type of flexible conduit and whether of not it qualifies as an EGC in 250.118. For larger FMC they're not required because the FMC is not considered an EGC.
    Rob
  4. #4
    Quote Originally Posted by MAC702 View Post
    480V, 600A, 24", 3" flexible conduit
  5. #5
    Quote Originally Posted by dmulhol925 View Post
    Straight sealflex connector and non-concentric penertration
  6. #6
    Join Date
    Jul 2003
    New Jersey
    Posts
    25,380
    No required, since it's 3" a wire type EGC is required.