Results 1 to 6 of 6

Thread: New Reliance Portable Generator Thru the Wall Kit

  1. #1
    Join Date
    Feb 2003
    Location
    Bremerton, Washington
    Posts
    7,606

    New Reliance Portable Generator Thru the Wall Kit

    Reliance has a new portable generator thru the wall kit
    >Power inlet
    >PVC conduit
    >Power panel , well a 6 plex receptacle with LEDs.

    Basically its a receptacle on the inside wired out to a power inlet.
    Brings power inside, eliminates cords thru doors. Clever and meets a need.
    Its catalog WKPBN30. More popular for homeowner install

    Here is it at Wallmart, $99.00
    https://www.walmart.com/search/?query=wkpbn30
    Moderator-Washington State
    Ancora Imparo

  2. #2
    Join Date
    Jul 2007
    Location
    Clark County, NV
    Posts
    183
    Smart, simple installation. I like it. I might have to try that out, or look for something similar just to see what's out there.

    I've used inlets on lots of stuff, but I like this package for a backup homeowner deal.

    It's $82 at Amazon with free shipping. I just ordered one to try out.

  3. #3
    Join Date
    Feb 2003
    Location
    Bremerton, Washington
    Posts
    7,606
    Exactly, might be an easy sell for those who are not ready for a transfer switch.
    Moderator-Washington State
    Ancora Imparo

  4. #4
    Join Date
    Jul 2007
    Location
    Clark County, NV
    Posts
    183
    Quote Originally Posted by tom baker View Post
    Exactly, might be an easy sell for those who are not ready for a transfer switch.
    I get asked all the time about generators and few want to go through that hassle. This is almost a no-brainer, especially for those just getting cheap general-purpose generators.

    I must admit I never got around to doing a transfer switch for myself, especially because most of the time my generator was an engine-driven welding machine mounted on the truck. Our power isn't out long enough for me to string extension cords through the garage, either. But I will do this and be able to recommend it to others if I like it. Good find.

  5. #5
    Join Date
    Jun 2016
    Location
    Tampa, FL, USA
    Posts
    936
    Here's a link to a video showing installation.

    https://www.youtube.com/watch?v=zR_hV75ASSk

    There does not appear to be any OCPD on any of the receptacles. The packaging says will handle a genny up to 7500 watts. That's 31 amps on each hot probably feeding three of the six 15 amp receps. How is this code compliant?

    The kit is for wood framed houses only. It won't work on a block, brick, metal building without extra tools.
    Last edited by Coppersmith; 10-11-17 at 11:21 PM.

  6. #6
    Join Date
    Aug 2004
    Location
    Northern illinois
    Posts
    15,578
    Quote Originally Posted by Coppersmith View Post
    Here's a link to a video showing installation.

    https://www.youtube.com/watch?v=zR_hV75ASSk

    There does not appear to be any OCPD on any of the receptacles. The packaging says will handle a genny up to 7500 watts. That's 31 amps on each hot probably feeding three of the six 15 amp receps. How is this code compliant?

    The kit is for wood framed houses only. It won't work on a block, brick, metal building without extra tools.
    does it need to be code compliant since it is not part of the premises electrical system?

    maybe it has CBs inside that distributes power to the receptacles.
    Last edited by petersonra; 10-12-17 at 11:01 AM.
    Bob

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •