Thread: Conduit sleeve for ground

  1. #11
    Join Date
    Dec 2010
    Posts
    1,325
    Quote Originally Posted by ActionDave View Post
    Because emt needs the extra bonding, because pvc doesn't, and because there's no need for any concealment.
    I agree with those.
    The more they overthink the plumbing, the easier it is to stop up the drain

  2. #12
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    33,749
    Also keep in mind if this is the grounding electrode conductor the splicing device used must be listed for grounding.

  3. #13
    Join Date
    Apr 2006
    Location
    Upstate S.C.
    Posts
    828
    If the conductor is bare, you don't need to bond at either/both ends is what I have always understood.
    It's my name going on that drawing, not yours. If what you want ain't right, it ain't going on the drawings!

  4. #14
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    33,749
    Quote Originally Posted by Ragin Cajun View Post
    If the conductor is bare, you don't need to bond at either/both ends is what I have always understood.
    Are you confident that any "casual" contact is a good enough bond?

  5. #15
    Join Date
    Aug 2004
    Location
    Northern illinois
    Posts
    15,683
    Quote Originally Posted by Ragin Cajun View Post
    If the conductor is bare, you don't need to bond at either/both ends is what I have always understood.
    but the code does not actually say that.
    Bob

  6. #16
    Join Date
    Jan 2007
    Posts
    2,963
    Quote Originally Posted by petersonra View Post
    I might hide it so some nitwit down the road does not notice it and try to "fix" it.
    Putting a sleeve over a ground splice would actually make it more noticeable.

    If a nitwit tried to "Fix a Splice" the only way he could actually "Fix it" would be to run a whole new conductor from point A to point B without the splice which would actually make him smarter than the nitwit that cut it short in the first place.

    I'm with Action Dave.

    Splice it and leave it like it is.

    JAP>

  7. #17
    Join Date
    Dec 2015
    Location
    United States
    Posts
    52
    It's a bare copper wire, it was also poured into the footer and is coming thru the slab, replacing it is somewhat of an issue

  8. #18
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    33,749
    Quote Originally Posted by karn View Post
    It's a bare copper wire, it was also poured into the footer and is coming thru the slab, replacing it is somewhat of an issue
    That is about the only time I splice such conductors.

  9. #19
    Join Date
    Dec 2014
    Location
    Sharps Chapel, TN
    Posts
    3
    My company failed an inspection due to something called dissimilar metals which would fit the application between copper and EMT. But as stated earlier in this forum all irreversible splices must be exposed so therevwould really be no need to have the splice covered by a piece of PVC conduit.


    Sent from my iPhone using Tapatalk

  10. #20
    Join Date
    Feb 2003
    Location
    Fl
    Posts
    16,722
    Quote Originally Posted by electrict dave View Post
    My company failed an inspection due to something called dissimilar metals which would fit the application between copper and EMT.
    So the inspector made you remove all copper EGC's from steel boxes and enclosures, interesting. How did you bond them?