  1. #1
    Join Date
    Dec 2015
    Location
    United States
    Posts
    44

    Conduit sleeve for ground

    The ground for the water main was cut short, I plan to use a hydraulic crimper to butt splice the 3/0 but would like to conceal the splice inside a short run of conduit, I planned to use 1" EMT and a colleague said by code it should be in PVC, is there any reason for this?

  2. #2
    Join Date
    Dec 2010
    Posts
    1,291
    Splices cannot be in raceway. It needs to be in a box or exposed.
    The more they overthink the plumbing, the easier it is to stop up the drain

  3. #3
    Join Date
    Aug 2004
    Location
    Northern illinois
    Posts
    15,573
    Quote Originally Posted by karn View Post
    The ground for the water main was cut short, I plan to use a hydraulic crimper to butt splice the 3/0 but would like to conceal the splice inside a short run of conduit, I planned to use 1" EMT and a colleague said by code it should be in PVC, is there any reason for this?
    as the other poster mentioned you cannot generally put a splice in a piece of conduit. pvc is handy for routing gecs because it does not have to be bonded.
    Bob

  4. #4
    Join Date
    Feb 2003
    Location
    Fl
    Posts
    16,626
    Quote Originally Posted by karn View Post
    The ground for the water main was cut short, I plan to use a hydraulic crimper to butt splice the 3/0 but would like to conceal the splice inside a short run of conduit, I planned to use 1" EMT and a colleague said by code it should be in PVC, is there any reason for this?
    Well it's not actually prohibited by code but you would need to bond both ends of the EMT to the conductor to negate the choke effect and with PVC this would not be a concern.

    Roger
    Moderator

  5. #5
    Join Date
    Aug 2004
    Location
    Northern illinois
    Posts
    15,573
    Quote Originally Posted by roger View Post
    Well it's not actually prohibited by code but you would need to bond both ends of the EMT to the conductor to negate the choke effect and with PVC this would not be a concern.

    Roger
    I think you might be right about hiding the splice in the EMT being OK since it is not being used as a raceway but as a sleeve. It would still have to be bonded, which makes the PVC idea maybe more attractive.

    300.13 Mechanical and Electrical Continuity — Conductors.
    (A) General. Conductors in raceways shall be continuous
    between outlets, boxes, devices, and so forth. There shall be no
    splice or tap within a raceway unless permitted by 300.15;
    368.56(A); 376.56; 378.56; 384.56; 386.56; 388.56; or 390.7.
    Bob

  6. #6
    Join Date
    Feb 2009
    Location
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    8,603
    I would not use emt under any circumstances and I wouldn't use pvc either unless I was ordered to. There is no reason to conceal the splice.
    Once in a while you get shown the light
    In the strangest of places if you look at it right. Robert Hunter

  7. #7
    Join Date
    Aug 2004
    Location
    Northern illinois
    Posts
    15,573
    Quote Originally Posted by ActionDave View Post
    I would not use emt under any circumstances and I wouldn't use pvc either unless I was ordered to. There is no reason to conceal the splice.
    why, why, and why?
    Bob

  8. #8
    Join Date
    Jun 2012
    Location
    NW Ohio
    Posts
    890
    Because....what are you trying to hide?

    You don't want the boss to readily see it, since you didn't measure so good.

  9. #9
    Join Date
    Aug 2004
    Location
    Northern illinois
    Posts
    15,573
    Quote Originally Posted by mopowr steve View Post
    Because....what are you trying to hide?

    You don't want the boss to readily see it, since you didn't measure so good.
    I might hide it so some nitwit down the road does not notice it and try to "fix" it.
    Bob

  10. #10
    Join Date
    Feb 2009
    Location
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    8,603
    Quote Originally Posted by petersonra View Post
    why, why, and why?
    Because emt needs the extra bonding, because pvc doesn't, and because there's no need for any concealment.
    Once in a while you get shown the light