    Bucket truck work . " Changing parking lot lights while energized " ???

    Have a contractor that is coming in with a bucket truck to change our parking lot metal halide lamps that are out . He wants to do this while energized . I say this is not allowed anymore . Just wondered if the contractors out there are doing this " HOT " . ???

  2. #2
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    33,498
    To just replace lamps might be acceptable.

    Then comes whether or not the guy is self employed or is an employee. Self employed are not subject to OSHA as they are not an employee.

    Your company could still require contractors on your property to comply with your companies safety policies though regardless of what they may or may not have for their own policies.

  3. #3
    Join Date
    Jun 2012
    Location
    NW Ohio
    Posts
    929
    Gets awfully difficult to troubleshoot problems with HID fixtures with the power off.

    Beside that he should be in an insulated bucket and using live voltage gloves to do testing if needed.

  4. #4
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    33,498
    Quote Originally Posted by mopowr steve View Post
    Gets awfully difficult to troubleshoot problems with HID fixtures with the power off.

    Beside that he should be in an insulated bucket and using live voltage gloves to do testing if needed.
    I agree that some of the troubleshooting tasks are live work tasks. Replacing a lamp may not be considered a live work task, replacing a ballast, capacitor, ignitor or lamp holder I would think would ordinarily require verifying there is no voltage before performing the task.

  5. #5
    Join Date
    Apr 2007
    Location
    Huntington Beach, CA (19 Hrs. 22 Min. from Winged Horses)
    Posts
    6,144
    Quote Originally Posted by Davebones View Post
    Have a contractor that is coming in with a bucket truck to change our parking lot metal halide lamps that are out . He wants to do this while energized . I say this is not allowed anymore . Just wondered if the contractors out there are doing this " HOT " . ???
    relamping is one thing.
    it would be nice to see it fire before lowering.
    don't see that as unsafe. what's 70E say about
    relamping where no live parts are present?

    pole lighting is usually 480 or 277 where available.
    sure... let's poke around in a 20 year old ballast with
    an old wasps nest in the top of the pole, hot. sounds
    like fun.
    ~New signature under construction.~
    ~~~~Please excuse the mess.~~~~

  6. #6
    Join Date
    Feb 2009
    Location
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    8,761
    Quote Originally Posted by Fulthrotl View Post
    relamping is one thing.
    it would be nice to see it fire before lowering.
    don't see that as unsafe. what's 70E say about
    relamping where no live parts are present?

    pole lighting is usually 480 or 277 where available.
    sure... let's poke around in a 20 year old ballast with
    an old wasps nest in the top of the pole, hot. sounds
    like fun.
    Funny and true at the same time. You have a knack for that.
    Once in a while you get shown the light
    In the strangest of places if you look at it right. Robert Hunter

  7. #7
    Join Date
    Jul 2008
    Location
    North Of Tampa Fl
    Posts
    406
    These are 480 volt , 400 watt metal halide type lamps

  8. #8
    Join Date
    Jul 2015
    Location
    Soldotna, AK, USA
    Posts
    36
    Quote Originally Posted by Davebones View Post
    Have a contractor that is coming in with a bucket truck to change our parking lot metal halide lamps that are out . He wants to do this while energized . I say this is not allowed anymore . Just wondered if the contractors out there are doing this " HOT " . ???
    Well de-energized does not make the task safe. It limits the risks with one aspect of the work electricity and it doesn't eliminate that risk.
    What about gravity? Is he tied off with the correct fall protection? Can people walk under his work area and have a tool dropped on them?
    What about LOTO? He turned it off but can someone turn it back on while he's in the lift?
    What about using mechanical means to move yourself into position? is the machine jerky? Is he experienced in it?
    What about gloves? Bulbs that are fragile and break when the base is corroded a little in the socket cut hands easy.
    What about glasses? Bulbs shatter...
    What about communication? Can he call someone to help him quickly?
    What about a the capacitor in the light fixture that can't be de-energized without touching it, does he know what they are and does he know the dangers of them?
    Does he have a ground guy? Does the ground guy know how to lower the boom with the emergency release switches on most lifts? Is someone able to see the guy in the lift in case he smushes himself into something?

  9. #9
    Join Date
    Jul 2008
    Location
    North Of Tampa Fl
    Posts
    406
    Didn't ask " What About " , Gravity , LOTO , Machine jerky , Gloves , Glasses , Communication ,Capacitor , ground guy , etc ... Was asking if contractors are working these while energized ! Have worked on jobs where someone was killed ( 4160V electrocution ) ( 277V electrocution ) ( 120V electrocution ) ( fall from D ring in Nuclear plant ) ( Fall from smokestack at coal plant ) ( Crushed by coal train unloading ) ( Fall from building steel ) ( 230KV electrocution ) ( Fall into sulfuric acid pit ) ( fell from JLG lift ) etc ...I try to be as safe as possible with contractors coming in . I know a lot of people think OHSA is overboard but I do know that the safety is better than when I started in the trade . The operator was trained , he had gloves , glasses , a ground man , a harness , a phone . When I started in the trade there wasn't training you went with a journeyman and learned that way . They wanted to change them while energized I said no . My question are contractors working these lights hot !

  10. #10
    Join Date
    Nov 2003
    Location
    The incredible, yet very expensive, Hudson Valley, NY NEC 2008
    Posts
    1,836
    I've been known to disconnect power in the hand hole at the pole base to perform my work. Ground man can reconnect for testing purposes.
    Mike, Dutchess County, NY