Thread: Lights come on for about 3 seconds then shut off. Tripping breaker

  1. #11
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    33,423
    Quote Originally Posted by Electric-Light View Post
    You don't have two neutral paths do you? If any portion of current is diverted into another neutral path, the GFCI will trip.
    But should trip immediately and not after 3 seconds.

    Capacitive leakage because of a long run could be an issue though.

  2. #12
    Join Date
    Feb 2007
    Location
    USA
    Posts
    5,318
    This sounds like a job in California, and a project with a jobsite trailer so I would assume permitted. So I would be these have 0-10v dimming being under the energy code. I would bet that this is temped in using a GFCI receptacle. There is probably a issue with current flowing back on another neutral or through the dimming.