    I have a fire damper that is penetrating the last floor (roof) and I need to know if we have to apply a fire sealant material around the damper just like we do in the walls between the rooms or it's not required.
    appreciate your help guys
  2. #2
    Join Date
    Jun 2017
    WI, USA
    Posts
    379
    You have not told us type of construction, but typically exterior envelope and between floors are required to have a fire rating. Reference the same plans that you are using to determine which wall penetrations require fire stop. Given this is a fire damper, I’d guess yes again.
  3. #3
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    38,232
    Quote Originally Posted by publicgood View Post
    same here.
  4. #4
    Join Date
    Oct 2016
    NY
    Posts
    8
    It's a concrete construction. I thought that in case of fire it wouldn't make a difference if the fire or smoke got it's way out of these penetrations since it's going outside the building through the roof and not affecting any other building.
  5. #5
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    38,232
    Quote Originally Posted by LAYTH-X View Post
    Why would the fire damper need to be there if there doesn't need to be a rating on this part of the building envelope?
    If a weak portion easily burns through before that 1 hour/ 2 hour rating period then you increase ventilation which allows more oxygen to fuel the fire.
  6. #6
    Join Date
    Oct 2016
    NY
    Posts
    8
    Quote Originally Posted by kwired View Post
    It's exhaust fan with a fire damper
  7. #7
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    38,232
    True fire damper or just a back-draft damper?
  8. #8
    Join Date
    Oct 2016
    NY
    Posts
    8
    True fire smoke damper