Results 1 to 8 of 8
Thread: GFI Equipment breakers
  1. #1
    Has anyone used the GFI equipment type breakers that trip at 30 miliamps on commercial coolers in restaurants ?
  2. #2
    Join Date
    Jan 2009
    3 Hr 2 Min from Winged Horses
    Posts
    14,212
    I have not. Is there a particular reason you want to?
    "Electricity is really just organized lightning." George Carlin
    Derek
  3. #3
    Join Date
    Jul 2003
    New Jersey
    Posts
    25,382
    Are you proposing using 30ma GFPE in lieu of 5ma protection that is required on receptacle circuits?
    Rob
  4. #4
    yes because the the 5 ma seem to trip easy on a cooler and heating elements and if i am reading the code right the 5 ma if for counter receptacles not equipment that stays plugged in
  5. #5
    Join Date
    Jun 2003
    NE (9.1 miles @5.07 Degrees from Winged Horses)
    Posts
    9,714
    Quote Originally Posted by Pauls Electric View Post
    I don't read it that way, can you be more specific?
    Tom
    TBLO
  6. #6
    Join Date
    Jul 2007
    Clark County, NV
    Posts
    1,098
    ...if i am reading the code right the 5 ma if for counter receptacles not equipment that stays plugged in
    You didn't put what Code cycle you are working with. Which exact article are we wanting to get on the same page on?
  7. #7
    Join Date
    Jul 2005
    LA basin, CA
    Posts
    1,808
    Sounds like commercial refrigeration equipment is calling for GFP protection, or someone wants to include it.
    Most 120v readings I find at energized refrigerator door handles are caused by defective light sockets or light switches.
    By the time I get there, workers were accustomed to working in the dark, using their phone flashlight, and bibs to grab the door handle.
    Its not until the owner himself grabs the door with his bare hands, and gets jolted on his butt, before someone finally calls.
    Roger Ramjet NoFixNoPay
  8. #8
    Join Date
    Jul 2003
    New Jersey
    Posts
    25,382
    You're reading it incorrectly, all receptacles in this location require GFCI protection (5ma, class A) whether they feed permanently installed equipment or counter receptacles.
    Rob
Posting Permissions
  • You may not post replies
  • You may not edit your posts