    Fire alarm NAC circuits

    I've come across strobes and horn/strobes speced to be wired alternating circuits..like a/b/a/b ...anyone familiar with this?

  2. #2
    Join Date
    Mar 2003
    Location
    Perry, Mi. Shiawassee
    Posts
    71
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    came across a speaker strobe that was labeled A/V throughout the drawings, never figured out why it wasn't labeled S/S.
    jerryalan

  3. #3
    Join Date
    Dec 2012
    Location
    Placerville, CA, USA
    Posts
    19,856
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by jerryalan View Post
    came across a speaker strobe that was labeled A/V throughout the drawings, never figured out why it wasn't labeled S/S.
    Cause it is an Audio/Visual device?

  4. #4
    Join Date
    Oct 2007
    Location
    New Jersey
    Posts
    6,264
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by GoldDigger View Post
    Cause it is an Audio/Visual device?
    Yes, that exactly.

  5. #5
    Join Date
    Oct 2007
    Location
    New Jersey
    Posts
    6,264
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by mstrlucky74 View Post
    I've come across strobes and horn/strobes speced to be wired alternating circuits..like a/b/a/b ...anyone familiar with this?
    It was popular in NYC, or so I've been told. The Port Authority of NY and NJ has added a design guideline for fire alarm systems for the LaGuardia Terminal B project that says you can't lose more than 60% of the notification appliances in a space if there is a circuit failure. There is nothing in NFPA 72, the NYC building code or Appendix Q thereto that requires "A/B" circuiting. It may show up in a specification, or there may be an AHJ who has a "shirt-pocket" rule.

  6. #6
    Join Date
    Sep 2012
    Location
    NJ
    Posts
    2,288
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by gadfly56 View Post
    It was popular in NYC, or so I've been told. The Port Authority of NY and NJ has added a design guideline for fire alarm systems for the LaGuardia Terminal B project that says you can't lose more than 60% of the notification appliances in a space if there is a circuit failure. There is nothing in NFPA 72, the NYC building code or Appendix Q thereto that requires "A/B" circuiting. It may show up in a specification, or there may be an AHJ who has a "shirt-pocket" rule.
    Gad just revisited this thread. It does look like NYC code requires alternating circuits for notification.
    Attached Images Attached Images

  7. #7
    Join Date
    Mar 2003
    Location
    New England
    Posts
    13,662
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I've seen it as a job spec but not written into any official local code.

  8. #8
    Join Date
    Oct 2007
    Location
    New Jersey
    Posts
    6,264
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by mstrlucky74 View Post
    Gad just revisited this thread. It does look like NYC code requires alternating circuits for notification.
    Where did you find your pages? It looks like it's out of the formal wording to amend a code, the clue being that all the words are underlined.