    While troubleshooting a heat trace circuit, I checked continuity between the two conductors. There was continuity, but is this because of the semi conductor or is it likely that there is a short in the wiring? The circuit was not working, but the breaker did not trip as if there was a dead short in the circuit.
  2. #2
    Join Date
    Jun 2003
    NE (9.1 miles @5.07 Degrees from Winged Horses)
    Posts
    9,167
    Quote Originally Posted by jmc24 View Post
    Use an ohm meter, you need to know the resistance of the circuit. Continuity checks are just that, continuity.
    Is there power applied to the cable?
    Tom
    TBLO
  3. #3
    Join Date
    Oct 2013
    newburgh,ny
    Posts
    422
    Check specs
    Heat trace has a ohms per foot rating I think. .And yes self limiting does use a semi conductor.
    A cowboy may get thrown , but they always get up and walk forward.
  4. #4
    Join Date
    Nov 2017
    Sullivan, IL
    Posts
    3
    Quote Originally Posted by ptonsparky View Post
    No, there was no power applied to the cable. Both ends of the cable were unhooked and open, so my assumption was that there should be no continuity between the 2 conductors. Is that correct?
  5. #5
    Join Date
    Oct 2013
    newburgh,ny
    Posts
    422
    The heat trace cable is the load. Think of it as a bunch of small heater elements, one end connected to each conductor repeat many times.
  6. #6
    Join Date
    Feb 2009
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    9,134
    Incorrect. The heat tape is conductive throughout its entire length. The two conductors have to stay clear of each other or else you'll get a short circuit.
    If you go and decide to dance with a gorilla the dance ain't over till the gorilla decides it's over.
  7. #7
    Join Date
    Dec 2006
    Eastern Oregon
    Posts
    3,451
    If it uses termination boxes at the end of the run, I would just put my meter on the terminals and very I had line voltage.
    If it doesn't use termination boxes at the end, I would instead test power at the starter box and verify line voltage and then ohm the cable as Ptonsparky suggested.
  8. #8
    Join Date
    Feb 2003
    Bremerton, Washington
    Posts
    7,723
    Heat cable has a negative temp coefficient, the colder the temp, the lower the resistance, hence more heat.
    Check mfgs literature, get the ohms per foot/deg F
    Moderator-Washington State