    DH Module
    When powering a door holder with 24v power from fire alarm system do you need a control module?
  2. #2
    Join Date
    May 2017
    SCV Ca, USA
    Posts
    324
    Quote Originally Posted by mstrlucky74 View Post
    According to Kyle J. Schuler:
    firealarmsonline.com/2013/05/FADoorHolderWithBatteryBackup.html
  3. #3
    Join Date
    Oct 2007
    New Jersey
    Posts
    5,706
    Mostly, yes. Or you can hook it up through a relay on the motherboard. I don't like putting things on the motherboard in case something ugly happens to the field conductors.
    The other way to do it is to hook it up to the aux power supply on a notification appliance circuit booster panel. These can usually be dip-switch programmed to drop out if the panel receives a signal to activate the notification appliances.
  4. #4
    Join Date
    Sep 2012
    NJ
    Posts
    1,994
    Thanks
  5. #5
    Join Date
    Sep 2012
    NJ
    Posts
    1,994
    So they can be powered via 24v not 120v?
  6. #6
    Join Date
    Feb 2003
    Fl
    Posts
    17,132
    Yes.
    Roger
    Join Date
    Oct 2007
    New Jersey
    Posts
    5,706
    Frequently they come with all three flavors: 24VDV, 24VAC, and 120VAC.