    Test tomorrow, one last question

    From PSI practice test, What is the minimum size copper conductor permitted for use for a 6,000 volt service? Answer is 6AWG. Where is a code reference to sizing wire based on voltage?
    Other than that I think I'm ready. head only moderately spinning from the last month of study. Thanks, Don

  2. #2
    Join Date
    Feb 2009
    Location
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    8,761
    Never heard of a 6000V service. You don't size wires based on voltage, you size them based on amperage. I've taken about nine PSI exams and never seen that question.
    Once in a while you get shown the light
    In the strangest of places if you look at it right. Robert Hunter

  3. #3
    Join Date
    Dec 2010
    Location
    Tennessee NEC:2008
    Posts
    4,224
    Quote Originally Posted by DonAJ View Post
    From PSI practice test, What is the minimum size copper conductor permitted for use for a 6,000 volt service? Answer is 6AWG. Where is a code reference to sizing wire based on voltage?
    Other than that I think I'm ready. head only moderately spinning from the last month of study. Thanks, Don
    6000V?
    If you aim at nothing, you will hit it every time!

  4. #4
    Join Date
    Jun 2017
    Location
    Kalispell, Mt
    Posts
    6
    6000V. That was cut and paste from the test. Your responses tell me what I needed to know, think it's a goof up question. Thanks Gents and to all a good night

  5. #5
    Join Date
    Jul 2007
    Location
    Clark County, NV
    Posts
    474
    That question and answer appear halfway down this page: https://quizlet.com/137528490/previo...s-flash-cards/

    I used the Find function for "6,000" to find it once I was on the page.

    Perhaps that will at least help, by looking at the source and other claimed "previous questions."

  6. #6
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    23,788
    Could be they were thinking of this:

    VIII. Services Exceeding 1000 Volts, Nominal230.200 General. Service conductors and equipment used
    on circuits exceeding 1000 volts, nominal, shall comply
    with all the applicable provisions of the preceding sections
    of this article and with the following sections that supple-
    ment or modify the preceding sections. In no case shall the
    provisions of Part VIII apply to equipment on the supply
    side of the service point.
    Informational Note: For clearances of conductors of over
    1000 volts, nominal, see ANSI C2-2007, National Electri-
    cal Safety Code.
    230.202 Service-Entrance Conductors. Service-entrance
    conductors to buildings or enclosures shall be installed to
    conform to 230.202(A) and (B).
    (A) Conductor Size. Service-entrance conductors shall not
    be smaller than 6 AWG unless in multiconductor cable.
    Multiconductor cable shall not be smaller than 8 AWG.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  7. #7
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    32,347
    Quote Originally Posted by infinity View Post
    Could be they were thinking of this:
    You got it,
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  8. #8
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    23,788
    Quote Originally Posted by Dennis Alwon View Post
    You got it,
    I think that since many of us don't deal with it on a regular basis that we tend to overlook the over 1000 volt stuff. IMO the 6000 volts is just there for confusion.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  9. #9
    Join Date
    Sep 2010
    Location
    Riverside, CA.
    Posts
    30
    How about 310.106(A) and Table 310.106(A).

    At 5001 to 8000 Volts the minimum copper conductor size is #6.

  10. #10
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    32,347
    Quote Originally Posted by Mouser View Post
    How about 310.106(A) and Table 310.106(A).

    At 5001 to 8000 Volts the minimum copper conductor size is #6.
    I guess that backs up what Trevor stated
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •