Hmmm... something I would stake my LIFE on? No.
There are these for MV cables, which will only be useful if NONE of the cables are energized:
http://www.davis.com/Product/HD_Elec...UaAqLXEALw_wcB
But they can't be used for anything under 2400V L-G and if there is a bundle of cables, it will not tell you WHICH one has a field around it. If it were me, I would ONLY start at one end and remove it, then use voltage meters to find the other end and remove it, then take out the KNOWN cable in verifiable chunks, even if it boils down to line of sight, no matter how long it took.
__________________________________________________ ____________________________
Many people are shocked when they discover I am not a good electrician...