    42P panel all with 1P 20A breakers(all #10 wire) and separate neutrals. Say there are about 7 homeruns with 6 circuits each.....all said and done with grounds there are about so about 91 #10 wires. So NECA and what we have used in the past is roughly about 5 minutes per wire. This includes dressing, tagging/labeling and terminations. So this is about 7-8 hours for all 91 wires. I know there are variables such as doing them all at once or going back and forth.
    Does 7-8 hours(basically one day) seem reasonable to you guys?
  2. #2
    Join Date
    Jul 2005
    Posts
    846
    Quote Originally Posted by mstrlucky74 View Post
    I always used .20 per pole, which includes the neutral....42 x .2 = 8.4 hrs
    What about your can labor?
  3. #3
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    37,928
    What tasks are you trying to cover?
    Just making up the panel after branch circuit conductors have been pulled and assuming the service/feeder supplying the panel has already been installed, it should only take 2 or 3 hours for anyone with experience to make up the connections in the panel. This also assumes whoever pulled conductors already had somehow identified what they go to and all you need to do is route, cut and terminate within the panel.
  4. #4
    Join Date
    Sep 2012
    NJ
    Posts
    2,156
    Quote Originally Posted by kwired View Post
    Agree but I'm talking total hours to term and identify/label wires...so I would add an hour or so to your 2-3
  5. #5
    Join Date
    Sep 2012
    NJ
    Posts
    2,156
    Quote Originally Posted by cdslotz View Post
    Can labor?? You mean the back box? That with trim and cover I use about 3 hours total. Remember guys these labor units represent other things as well...such as drawing study, material transport, layout, non productive labor. Only about 50% of the labor unit is actual instalttion.
  6. #6
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    37,928
    That is why I asked what tasks you are trying to cover, if you already covered material transport, layout etc. in another portion of the project you don't need to add it again to this task or group of tasks. Now if someone pulled conductors but didn't identify them then you have more to do with this task - but those pulling conductors did save some of their time not identifying things, though it may have been more efficient time management for them to do it then the guy that comes in later to sort things out. Might make a difference who gets paid the higher wages also.