LB 2 Inch

Status
Not open for further replies.

wirenut46

Member
Location
United States
?I have a 2 inch lb 63 cubic inches diameter. It is on the outside of a house under a disconnect looks like somebody changed the service. It has a piece of SER Cable in it with three 250 kcmils and a ground i need to know how to calculate this its seems to be very small to me. Thanks.:?
 
Last edited:

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Most LB's that size have the wire size stamped on it but if the wire is there you won't be able to see it. I think it is 4 --3/o conductors
 

wirenut46

Member
Location
United States
Thank You.

Thank You.

Thanks Dennis you are right i tried to look im going to change it this week two a 2.5 inch... I looked in the 2.5 inch and it stated 300 kcmill... I like the hippy stuff dude i used two own for smoke shops.
 

nizak

Senior Member
Conductor fill may be ok but you might want to check the minimum bending radius if it's installed in the form of a jacketed SER cable.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Conductor fill may be ok but you might want to check the minimum bending radius if it's installed in the form of a jacketed SER cable.

I agree, in almost every scenario SE cable is an LB conduit body is a violation.
 