    Quote Originally Posted by Ingenieur View Post
    really?

    we know this
    1000 hp
    4000 v
    122 a
    I think it would be 4160V on the nameplate.

    An example:

    Last edited by GoldDigger; 11-12-17 at 05:01 PM. Reason: Speling in title: your --> you're
    Si hoc legere scis nimium eruditionis habes.

  2. #2
    Join Date
    Jan 2016
    Location
    PA
    Posts
    4,039
    Quote Originally Posted by Besoeker View Post
    I think it would be 4160V on the nameplate.

    An example:

    the catalog lists them at 4000
    every one I've seen is rated at 4000, and I've seen 100's



  3. #3
    Join Date
    Jan 2016
    Location
    PA
    Posts
    4,039
    another
    these are mine fans
    we need more info



  4. #4
    Join Date
    Sep 2008
    Location
    UK
    Posts
    10,221
    Quote Originally Posted by Besoeker View Post
    I think it would be 4160V on the nameplate.

    An example:

    Please take heed of what the mod has posted.
    Si hoc legere scis nimium eruditionis habes.

  5. #5
    Join Date
    Sep 2008
    Location
    UK
    Posts
    10,221
    Quote Originally Posted by mike_kilroy View Post
    Nonsense. OP already said xfmr ratio is adjustable.
    But we don't know if it was adjusted.
    Si hoc legere scis nimium eruditionis habes.

  6. #6
    Join Date
    Sep 2008
    Location
    UK
    Posts
    10,221
    Quote Originally Posted by Ingenieur View Post
    assume at motor
    Perhaps we should wait for factual data rather than make assumptions.
    Si hoc legere scis nimium eruditionis habes.

  7. #7
    Join Date
    Jan 2016
    Location
    PA
    Posts
    4,039
    why do technical posts keep getting censored?
    who believes the kva would not increase?
    875 kva xfmr rating
    840 kva load
    4000 vac
    121 a line and 70 a phase
    so Z = 57 ohm
    if dropped to 52 ohm would delivered kva increase or stay at 840?
    even if a 25% increase (120% of rating)?



  8. #8
    Join Date
    Feb 2016
    Location
    Illinois
    Posts
    487
    I can see a reality show on the horizon...."Big Brother, Nerd Edition".

  9. #9
    Join Date
    Jun 2004
    Location
    Cherry Valley NY, Seattle, WA
    Posts
    3,245
    I'd like to see how a utility would size their transformer to feed that load
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"

  10. #10
    Join Date
    Nov 2007
    Posts
    791
    Quote Originally Posted by electrofelon View Post
    I'd like to see how a utility would size their transformer to feed that load
    Good if the drive used is 12-pulse. Knowing that a 6-pulse drive will have a very high harmonics content. Remember that a 6-pulse drive with 2-3% line reactor will have to derate the supply transformer by approximately 85%. Loading the transformer more than 85% (which the OP did) gives no margin for extra load capacity.