    Class A is return loop. I know for smokes, etc. you have the return loop. Would you also have them for the NAC loop? Sometimes they are wired alternating circuit..A/B/A/B where I assume there is no return. Thanks.
  2. #2
    Join Date
    Mar 2010
    Lake of the Ozarks
    Posts
    1,041
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Yes, There is a return loop instead of an EOL when wired Class A
    1N73LL1G3NC3 15 7H3 4BILI7Y 70 4D4P7 70 CH4NG3.
  3. #3
    Join Date
    Mar 2003
    New England
    Posts
    13,662
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Here we are required to wire everything Class A by state code.
  4. #4
    Join Date
    Oct 2007
    New Jersey
    Posts
    6,238
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by luckylerado View Post
    Agreed, just be sure to check the installation instructions. Some panels still require the EOL; it's just installed at the panel.