    Service upgrade/relocation, no location for ground rods!?

    Picture a small town, downtown Main Street. The old Coast To Coast hardware store. Concrete/brick building, basement, main level, and upstairs. A fairly run down building. Concrete in alley, buildings butt up each side.

    Planning to install service on back of building in alley. Have a long run through bsmt to hit waterline with #4. Have no clue how to deal with ground rods! Everything is concrete!

    Anybody have any ideas before I cry to the inspector?!

    Thanks!

  2. #2
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    23,770
    Sounds like you'll have to make some holes in the concrete.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  3. #3
    Join Date
    Jun 2006
    Location
    NoDak
    Posts
    183
    That's what I'm thinking! Guess I'll have to do a locate so I choose a location that avoids gas and sewer lines!

  4. #4
    Join Date
    Jun 2015
    Location
    texas
    Posts
    1,571
    Quote Originally Posted by sw_ross View Post
    That's what I'm thinking! Guess I'll have to do a locate so I choose a location that avoids gas and sewer lines!
    Its a long shot, but here it is anyway...

    Check out 250.52 (A)(2) thru (8)

    Scroll thru the list and see if you have /can do any of those listed- if you do, then you already have your supplemental electrode- so you wouldn't have to add a rod.

    If you don't, then its rotary hammer time.
    Last edited by user 100; 11-12-17 at 08:19 PM. Reason: clarification