    when I get an GEC to transformer

    When in Canada, The GEC to the transformer, so the first point I connect is to the neutral or the equipment grounding? And what's the difference if I reverse the order?


    从我的 iPhone 发送,使用 Tapatalk

  2. #2
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    23,770
    You can do it either way. If landing on the grounding terminal and the system bonding jumper is a wire or bus bar then the SBJ and GEC both terminating there that is one option. Otherwise you can land the GEC directly on the X0.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  3. #3
    Join Date
    Oct 2017
    Location
    多伦多
    Posts
    3
    Quote Originally Posted by infinity View Post
    You can do it either way. If landing on the grounding terminal and the system bonding jumper is a wire or bus bar then the SBJ and GEC both terminating there that is one option. Otherwise you can land the GEC directly on the X0.
    So there is no difference between this two option?


    从我的 iPhone 发送,使用 Tapatalk

  4. #4
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    23,770
    Quote Originally Posted by kylelee View Post
    So there is no difference between this two option?

    Not much and the NEC gives you the choice as to how it's done. Bonding the neutral at the disconnect will allow some of the neutral current to flow on the raceway if it's metal.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted