    OLSUN transformer Wire connection

    I have a 5KV-480-208/120 dry type transformer manufactured by OLSUN -USA . The size of primary wires ( H1 , H2 , H3 ) and Secondary wires ( X0 , X1 , X2 , X3 ) is 14 AWG . The primary cable is 4C x 4 MM2 ( 12AWG ) and secondary cable is 4C x 35 MM2 ( 2AWG) . Both cables are XLPE/SWA/PVC . For terminations inside the transformer , Does NEC allow using wire nut or I can use terminal lugs with one hole with bolt and nuts with heat shrinkable tube , rubber tape and electrical tape . I could not find a manual on OSLUN website .
    Attached Thumbnails Attached Thumbnails Click image for larger version. 

Name:	IMG_6259.jpg 
Views:	36 
Size:	95.5 KB 
ID:	18932   Click image for larger version. 

Name:	IMG_6348.jpg 
Views:	29 
Size:	119.6 KB 
ID:	18933   Click image for larger version. 

Name:	olsun.jpg 
Views:	27 
Size:	116.1 KB 
ID:	18934  

  2. #2
    Join Date
    Feb 2003
    Location
    Fl
    Posts
    16,681
    Wire nuts are fine.

    Roger
    Moderator

  3. #3
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    23,770
    I agree with Roger, I would use wire nuts also on those small conductors but you may have a problem if your using #2 AWG conductors..
    Rob

    Moderator