    Quote Originally Posted by infinity View Post
    The primary disconnect is OK on another floor (distance is irrelevant) if the transformer is labeled with the location of the primary disconnect. Generally the secondary condcutors are limited to 25' without overcurrent protection so at 100' you may have a problem
    Quote Originally Posted by jap View Post
    Just to add to this,,,, adding a "disconnect" as stated in the OP on the secondary is not going to solve your problem.

    JAP>
    True and I did say that you need an OCPD within 25' so the disco would need fuses.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  2. #12
    Join Date
    Jan 2007
    Posts
    2,903
    Quote Originally Posted by infinity View Post
    True and I did say that you need an OCPD within 25' so the disco would need fuses.
    Yea, but you gave away the farm too early,,,, I have to post 30 times before anyone ever gives up any valuable information.

    JAP>