Is it Possible to take 6 poles to feed one circuit breaker for PanelBoard

Status
Not open for further replies.

leskfee19

Banned
Location
Indiana
Hi all,

I do have a Distribution Panel With 8 branch circuit breakers (hree phase) whith rate 160 Ampere & 220/110 Volt so I would like to connect two circuit breakers from Distribution Panel to feed one panelboard with rate of 400 Ampere?
So is it possible to have two circuit breakers (6 pole) connect to one panel board?


thanks a lot
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Not allowed. 240.8 limits circuit breakers from being connected in parallel other than listed factory assembled units.
 
Location
NE (9.06 miles @5.9 Degrees from Winged Horses)
Occupation
EC - retired
Hi all,

I do have a Distribution Panel With 8 branch circuit breakers (hree phase) whith rate 160 Ampere & 220/110 Volt so I would like to connect two circuit breakers from Distribution Panel to feed one panelboard with rate of 400 Ampere?
So is it possible to have two circuit breakers (6 pole) connect to one panel board?


thanks a lot

Yes, it is possible. You can also step into the path of a freight train.

Should you? Absolutely not.

Ref: NEC 240.8
 

leskfee19

Banned
Location
Indiana
thanks a lot for your help!

in fact that for a (project Site!
what about voltage that go thru 6 poles (output) to 3 phase input main C.K.

thx
 