Hello All,
I decided to make this a new post. I'm having issues with inspectors.
I'm building a pool on a lot where overhead high voltage runs through the back property line for which my setback for a pool is 7.5 feet.
I have over 22.5 clearance from these lines. However, the inspector is saying I need 10 feet horizontal as referenced in 680.8. From all the posts here, I have interpreted 680.8 to mean that if you don't have 10 feet horizontal clearance, you need 22.5 feet overall clearance in ANY direction. And vice versa, if you don't have 22.5 clearance, you at least need 10 feet horizontal.
Am I right? This doesn't read clear at all in the code. Any references to help out?
Thanks so much! Cheers
I decided to make this a new post. I'm having issues with inspectors.
I'm building a pool on a lot where overhead high voltage runs through the back property line for which my setback for a pool is 7.5 feet.
I have over 22.5 clearance from these lines. However, the inspector is saying I need 10 feet horizontal as referenced in 680.8. From all the posts here, I have interpreted 680.8 to mean that if you don't have 10 feet horizontal clearance, you need 22.5 feet overall clearance in ANY direction. And vice versa, if you don't have 22.5 clearance, you at least need 10 feet horizontal.