    Mean of disconnect of transformer primary disconnect distance?

    I can't find any length requirement

    Is the disconnect for the transformer is within LOS (<15ft?), the disconnect does not required a lockable disconnect. However if the disconnect is non-LOS, it should be marked and lockable. Is there a requirement how far the disconnect can be for the primary side?

  2. #2
    Join Date
    Feb 2003
    Location
    Illinois
    Posts
    23,281
    There is no rule in the NEC that specifies a distance from the transformer for the primary disconnect.
    Don, Illinois
    Ego is the anesthesia that deadens the pain of stupidity. Dr. Rick Rigsby