    Ambient Temperature Correction factors

    I am running conductors in conduit outdoors (not underground) and would like to apply the ambient temperature correction factors in Table 310.15(B)(2)(a). Problem is the NEC doesn't specifically state HOW the ambient temperature is found. Any suggestions? Any tables or websites I could use?

  2. #2
    Join Date
    Sep 2010
    Location
    Riverside, CA.
    Posts
    30
    310.15(B)(3)(5) Informational Note:

    Informational Note: One source for the ambient temperatures
    in various locations is the ASHRAE Handbook — Fundamentals.

  3. #3
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    23,770
    I've heard a few different interpretations, one says that you use the yearly average temperature.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  4. #4
    Join Date
    Jul 2015
    Location
    Sunnyvale, CA USA
    Posts
    49
    Quote Originally Posted by Mouser View Post
    310.15(B)(3)(5) Informational Note:

    Informational Note: One source for the ambient temperatures
    in various locations is the ASHRAE Handbook — Fundamentals.
    Just as you responded I found this info in the ASHRAE handbook. Thanks!

  5. #5
    Join Date
    Oct 2009
    Location
    Austin, TX, USA
    Posts
    8,460
    Quote Originally Posted by minesh21 View Post
    Just as you responded I found this info in the ASHRAE handbook. Thanks!
    You can also go here: http://www.solarabcs.org/about/publi...map/index.html

  6. #6
    Join Date
    Jul 2015
    Location
    Sunnyvale, CA USA
    Posts
    49
    Quote Originally Posted by ggunn View Post
    Woah this is perfect. Thanks!