    4" Duct "Y" For 2 - Bath Fans

    Does anyone know of a 4" Duct "Y" that one can use in order to exhaust 2 - bath fans out of a single 4" wall vent?

    Thank you,
    Ravenvalor
    Electrical Contractor
    Piedmont Region of NC

    "Good day and good premises." (Ayn Rand)

  2. #2
    Join Date
    Feb 2003
    Location
    Somewhere over the rainbow
    Posts
    3,244
    Edward
    The only thing I know, is the progressive discovery of my ignorance


  3. #3
    Join Date
    Oct 2007
    Location
    Piedmont region of NC
    Posts
    717
    Quote Originally Posted by edward View Post
    The private home inspector turned down something similar to what yours looks like. He said that it was against code to run 2 - ducts out of a single wall vent. I plan to call the building inspector tomorrow for verification. I was hoping to find something like yours but with 2 - back draft dampers built into it. Thanks.
    Ravenvalor
    Electrical Contractor
    Piedmont Region of NC

    "Good day and good premises." (Ayn Rand)

  4. #4
    Join Date
    Apr 2007
    Location
    Huntington Beach, CA (19 Hrs. 22 Min. from Winged Horses)
    Posts
    6,138
    Quote Originally Posted by Ravenvalor View Post
    The private home inspector turned down something similar to what yours looks like. He said that it was against code to run 2 - ducts out of a single wall vent. I plan to call the building inspector tomorrow for verification. I was hoping to find something like yours but with 2 - back draft dampers built into it. Thanks.
    panasonic inline fans come with what you are looking for...
    a 4" wye, with flappers on each of the branches.

    so, they can be found.
    ~New signature under construction.~
    ~~~~Please excuse the mess.~~~~

  5. #5
    Join Date
    Oct 2007
    Location
    Piedmont region of NC
    Posts
    717
    Quote Originally Posted by Fulthrotl View Post
    panasonic inline fans come with what you are looking for...
    a 4" wye, with flappers on each of the branches.

    so, they can be found.
    Looks promising. I will let you know what the city inspector says. Thanks.
    Ravenvalor
    Electrical Contractor
    Piedmont Region of NC

    "Good day and good premises." (Ayn Rand)

  6. #6
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    33,423
    Quote Originally Posted by Ravenvalor View Post
    The private home inspector turned down something similar to what yours looks like. He said that it was against code to run 2 - ducts out of a single wall vent. I plan to call the building inspector tomorrow for verification. I was hoping to find something like yours but with 2 - back draft dampers built into it. Thanks.
    The fans typically already have back draft dampers included so you shouldn't need one in your wye.

    That said when both are running you may not get the airflow you would if each were separately vented or if they combined into a larger common duct.

  7. #7
    Join Date
    Jul 2007
    Location
    Clark County, NV
    Posts
    440
    Quote Originally Posted by kwired View Post
    ...combined into a larger common duct.
    Will also make the fans quieter, which may be required if spec'd for their noise level.

  8. #8
    Join Date
    Apr 2003
    Location
    Fort Collins, Colorado
    Posts
    1,567
    Quote Originally Posted by Ravenvalor View Post
    The private home inspector turned down something similar to what yours looks like. He said that it was against code to run 2 - ducts out of a single wall vent. I plan to call the building inspector tomorrow for verification. I was hoping to find something like yours but with 2 - back draft dampers built into it. Thanks.
    Not a mechanical code violation for 2 bath fans exhausts to "Y" together. Dryer & other exhaust, yes. And, certainly NOT an electrical problem.
    Ron

  9. #9
    Join Date
    Oct 2007
    Location
    Piedmont region of NC
    Posts
    717
    Quote Originally Posted by rcarroll View Post
    Not a mechanical code violation for 2 bath fans exhausts to "Y" together. Dryer & other exhaust, yes. And, certainly NOT an electrical problem.
    yes sir the local inspector agrees as long as its a Y And not a T

    Thanks
    Ravenvalor
    Electrical Contractor
    Piedmont Region of NC

    "Good day and good premises." (Ayn Rand)

  10. #10
    Join Date
    Nov 2017
    Location
    Southport, NC, USA
    Posts
    5
    Not a code violation, but at the end of the day AHJ overrides applicable code, so best bet is to consult if you're in doubt..