    Electrolysis

    I have had local plumbers talking about multiple job locations of pin holes in copper water lines. They are telling there customers that it is caused by electrolysis and want the owners to have an electrician correct the problem by disconnecting the bonded water lines. One case had green tinted water and also blamed electrolysis. What is this, how do you determine electrolysis, and ultimately how do you fix the problem... Any help?

  2. #2
    Join Date
    Jun 2003
    Location
    Hawthorne, New York NEC: 2014
    Posts
    3,163
    We get this question about every 6 months. Cut to the chase answer- it isn't an electrical problem but a water chemistry problem.

    -Hal

  3. #3
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    33,423
    If the problem is from electrical issues - it will be a DC current that you are trying to eliminate from the water piping.

    I agree most such issues are probably water chemistry problems and not electrical problems.

  4. #4
    Join Date
    Jun 2003
    Location
    NE (9.1 miles @5.07 Degrees from Winged Horses)
    Posts
    8,859
    Sometimes it is caused by poor practices of the installing plumber. Galvanized fittings mixed with Cu. High water flow. Excessive flux at soldering.

    Read up and go on the service call. Use the search feature at the upper right.
    Tom
    TBLO

  5. #5
    Join Date
    Dec 2012
    Location
    Placerville, CA, USA
    Posts
    18,366
    Quote Originally Posted by ptonsparky View Post
    S...
    Use the search feature at the upper right.
    Or if, as often happens, the Forum search feature is not doing a very good search, try a Google search which also includes the qualifier site:mikeholt.com.

  6. #6
    Join Date
    Jan 2007
    Location
    Great White North
    Posts
    399
    We maybe bucking the general consesus of this group but we have found the following.

    This problem seems to be more prevalent when supplied with well water.(possibly chemistry)

    We have found several 20 to 30 floor condo buildings with blue/green water and a sulphur type smell from the water. Ac current flow on the copper water piping throughout these buildings was 20 to 30 amps.

    When the AC current flow problem on the piping was corrected the problems gradually disappeared to eventually an acceptable condition.
    May the force be with you

  7. #7
    Join Date
    Jun 2003
    Location
    NE (9.1 miles @5.07 Degrees from Winged Horses)
    Posts
    8,859
    Quote Originally Posted by ghostbuster View Post
    We maybe bucking the general consesus of this group but we have found the following.

    This problem seems to be more prevalent when supplied with well water.(possibly chemistry)

    We have found several 20 to 30 floor condo buildings with blue/green water and a sulphur type smell from the water. Ac current flow on the copper water piping throughout these buildings was 20 to 30 amps.

    When the AC current flow problem on the piping was corrected the problems gradually disappeared to eventually an acceptable condition.
    Twenty to thirty amps is excessive and opens a whole new can of worms. Removing the bond is more likely to cause a shocking problem. Blue water or death? What shall we do? Find the problem as you have done and fix it. Removing the bond is incorrect.
    Tom
    TBLO

  8. #8
    Join Date
    May 2014
    Location
    AZ
    Posts
    2,090
    1) have the water tested to see what the supply has in it
    2) what type of copper, are the pipes stamped with type/maker

  9. #9
    Join Date
    Feb 2009
    Location
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    8,752
    Quote Originally Posted by ptonsparky View Post
    Twenty to thirty amps is excessive and opens a whole new can of worms. Removing the bond is more likely to cause a shocking problem. Blue water or death? What shall we do? Find the problem as you have done and fix it. Removing the bond is incorrect.
    Well said.
    Once in a while you get shown the light
    In the strangest of places if you look at it right. Robert Hunter

  10. #10
    Join Date
    Feb 2003
    Location
    Bremerton, Washington
    Posts
    7,636
    I work for a large municipal water system. Almost always, copper corrosion is caused by water chemistry, primarily low pH. Low pH water is very aggressive and erodes the protective oxide film that copper has, same with lead (what happened in flint is they did not have corrosion control)
    In about 1995 the EPA had the lead and copper rule, requiring testing certain homes (depending on when built) for corrosion issues. We started corrosion control in 1999 and we raise the pH from about 8-.0 to 8.5. Testing since then shows it has been very successful.

    Its not an electrical issue, I have the definitive study from the AWWA, that shows that. Your plumbers can always add a length of PVC pipe on the service line to isolate it if its is metallic to the water main.

    And have them do this, check with their water provider, ask for the consumer confidence report, look for the information on lead and copper.
    Or if on a private system have a water test done.